Modine Hot Dawg won't fire up

Beeffajitas

Member
Joined
Nov 13, 2012
Messages
6
Location
Southern NH
So, going through the pre-cold rituals. Had propane delivered today. Tried to fire up the Modine in the shop. It's not making all the relay/solenoid clicking that it usually does. In the past I have had to cycle the starting sequence to purge air from the propane line, but with no clicking I don't think I've even got to that point. Distribution blower fan will turn on.

Things I've tested so far..
- transformer is producing 24V to the board
- Honeywell control valve LED does light green (it's getting 24V) (no blinking)
- 120V is NOT going to the exhaust fan, after call for heat

Any thoughts?
 
To avoid these ads, REGISTER NOW!

Specracer

Well-known member
Joined
Nov 12, 2016
Messages
271
Have you killed power to the unit (causing a reboot)? And there are not any fault codes blinking?
 
To avoid these ads, REGISTER NOW!

D45

Well-known member
Joined
Mar 21, 2014
Messages
4,834
Location
NW INDIANA
Try checking the blade fuse inside, my friend had one bad from factory

$2 later it worked perfectly

Check for fault codes

What size unit?
 
OP
B

Beeffajitas

Member
Joined
Nov 13, 2012
Messages
6
Location
Southern NH
It's a HD-45AH

I'm not seeing a very complicated control board. I think all the controls happen inside the Honeywell control valve. It's P/N 5H76383.

Looks like this:
https://controlscentral.com/eCatalog/tabid/63/Category/Heating-Gas-Control-Valves/ProductID/506368/PageIndex/14/ViewType/2/Default.aspx

There's one LED on the Honeywell, no blinking. There is a sticker in the unit to identify codes.

This is the only board I see:
https://www.qcsupply.com/20886-modine-terminal-board-with-time-delay-relay.html

I did shut power off a couple of times.

I'm thinking this board is supposed to send a signal to the control valve to start the sequence, but I'm not sure how to test that.
 
Last edited:

JeepJohn62

Well-known member
Joined
Feb 25, 2019
Messages
157
Location
Alaska
So, going through the pre-cold rituals. Had propane delivered today. Tried to fire up the Modine in the shop. It's not making all the relay/solenoid clicking that it usually does. In the past I have had to cycle the starting sequence to purge air from the propane line, but with no clicking I don't think I've even got to that point. Distribution blower fan will turn on.

Things I've tested so far..
- transformer is producing 24V to the board
- Honeywell control valve LED does light green (it's getting 24V) (no blinking)
- 120V is NOT going to the exhaust fan, after call for heat

Any thoughts?
Is the unit firing up?, but the fan will not function, so it shuts off? I might be able to help. Just fixed mine this week.

Sent from my SM-A102U using The Garage Journal mobile app
 