Transition from in wall electrical wiring to EMT

branimal

Well-known member
Joined
May 31, 2016
Messages
1,955
I’m running a circuit from a standard 1900 box behind drywall and then across an area of exposed brick and then back to 1900 box behind drywall.

I’m going to use 1/2” EMT on the exposed brick wall.

How do you make that transition? Can I buy a drywall faceplate that has both an outlet cutout and a 1/2” knockout for EMT?

Or is there a better way to make that transition.


0f7828c467afc2092fa55b89858d3b41.jpg




Sent from my iPhone using Tapatalk
 

Attachments

  • 0f7828c467afc2092fa55b89858d3b41.jpg
    0f7828c467afc2092fa55b89858d3b41.jpg
    94.8 KB · Views: 3
To avoid these ads, REGISTER NOW!

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
Use box extensions:
Z_DKGxfo5oy.JPG
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
It looks like your wall is open. Before you drywall, remove that 1900 box from the stud and just stub the mc cable out. Once it is drywalled, surface mount a 1900 on the wall , bring the cable in the back of the box, and continue with your conduit. This way will eliminate all the extension and mud rings.

Sent from my SM-G960U using The Garage Journal mobile app
 
Last edited:
OP
B

branimal

Well-known member
Joined
May 31, 2016
Messages
1,955
ard; said:
Can't go up to the ceiling and across? Or under?


I want to put an outlet on the exposed brick fireplace for a tv.



Sent from my iPhone using Tapatalk
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
There many different ways of doing this. Is there a basement under there. Keep the box recessed in the wall, drop down in the basement with cable, stub up a piece of conduit on the brick for a surface mounted box, bring the cable into the conduit with the correct fitting. This will minimize the amount of conduit that you see.

Sent from my SM-G960U using The Garage Journal mobile app
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
There many different ways of doing this. Is there a basement under there. Keep the box recessed in the wall, drop down in the basement with cable, stub up a piece of conduit on the brick for a surface mounted box, bring the cable into the conduit with the correct fitting. This will minimize the amount of conduit that you see.

Sent from my SM-G960U using The Garage Journal mobile app

Except that you can't run cable in conduit except for sleeving purposes.

Tommy
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Except that you can't run cable in conduit except for sleeving purposes.

Tommy

This would be sleeving purposes. receptacle is only stubbed up a foot or so. Or a box could be installed on the bottom of conduit in basement to switch to a different style conductor. You could even pipe it the whole way and install THWN.

Edit: It didn't really say in the first post about going above a fireplace, just saw that in post #7. So going down in the basement wouldn't be practical. I would try to do it with the least visible conduit
 
Last edited:

AntonLargiader

Well-known member
Joined
Nov 20, 2016
Messages
1,372
Location
Charlottesville, VA
What's in the fireplace? Going to be a gas insert? I'm assuming since you're usually posting about apartments in Brooklyn it's not going to be burning wood, so maybe you can run the wires inside the chimney and do away with the exposed conduit altogether? Recessing an outlet box into a brick wall isn't hard at all.
 
To avoid these ads, REGISTER NOW!

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
This would be sleeving purposes. receptacle is only stubbed up a foot or so.

I'm pretty sure once you put a box on the end it is no longer sleeving, it's conduit. I was taught sleeving is when the tubing doesn't attach to anything on either end and is open. You use it to go through a masonry wall or for protecting the cable in an exposed area where it may be damaged.

I could be wrong.

Tommy
 
Last edited:

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
I'm pretty sure once you put a box on the end it is no longer sleeving, it's conduit. I was taught sleeving is when the tubing doesn't attach to anything on either end and is open. You use it to go through a masonry wall or for protecting the cable in an exposed area where it may be damaged.

I could be wrong.

Tommy

I meant you could put a box on the end if switching to a different wiring method. Or if using NM-B, with just a short distance, we put a bang on plastic bushing on the end and run the cable in the short piece of pipe to the device. We do this all the time when installing a laundry receptacle or a electric dryer circuit or a sump pump circuit in an unfinished basement. we stub a piece of conduit down from the joist, mount it on the concrete wall. no fitting on the top, just a plastic bushing. This is how it is done here, and it passes inspection, just short distances, to protect it from physical damage. Not saying it would fly elsewhere
 
Last edited:

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,924
Location
NW Iowa
It's not a conduit system if there isn't pipe from box to box. A piece of conduit running several feet above a box is done all the time to protect Romex.

The code does not prohibit Romex in conduit at all. If you have conduit from box to box you can run Romex. Not sure why you would want to but you could. Conduit fill can become an issue if you run Romex in conduit, sleeve or not.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
It's not a conduit system if there isn't pipe from box to box. A piece of conduit running several feet above a box is done all the time to protect Romex.

The code does not prohibit Romex in conduit at all. If you have conduit from box to box you can run Romex. Not sure why you would want to but you could. Conduit fill can become an issue if you run Romex in conduit, sleeve or not.

An illustration from Mike Holt showing the rules for sleeves.
138864-nm-cables-entering-panel-through-flexible-metal-conduit-nm-requirements-nec-wire-clamp-termination-requirements-where-nm-cables-enter-panel_t_11468-02.jpg
 

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
Question...could he run flex in the wall, into a connector- which is screwed into the 'back' size of an LB. LB is exposed with EMT running from there. No splices; conductors are continupous from box to box...

shopping


shopping


shopping


shopping






Wondering...
 
Last edited:
To avoid these ads, REGISTER NOW!
Top Bottom