Ok guys speak to me like I’m retarted in this situation. I have zero idea how to add the section of pipe to cure the water hammer.
Is it one per valve? I have 4 valves.
How do you do the water hose trick? Any pictures?
I have made my own by simply adding a capped section of pipe filled with trapped air.
The largest was concealed as a post to support a clothes line.
If my memory is correct it was 1966, in Southern Spain.
Increase the pipe size or decrease the sprinklers per zone. You're flowing more gpms that the pipe is rated for. The high velocity is causing the hammer.
I don't see the pipe sizes or number of sprinklers stated so I don't know how you came to that conclusion. It's a common problem and the usual way to fix it is to install a shock arrestor of some kind.
Interesting video with good basic principles. Increasing the pipe size does decrease the effect but for something already in place it may be impractical. Same with reducing the number of sprinklers on a zone. Given that the OP hasn't given more detail it's hard to know what would solve the problem with the least trouble/cost.
If it's always been an issue that is likely the cause. Exceeding recomend velocity leads to water hammer. A shock arrestor is a good bandaid. I was suggesting a different approach. I suppose more info is needed.I don't see the pipe sizes or number of sprinklers stated so I don't know how you came to that conclusion. It's a common problem and the usual way to fix it is to install a shock arrestor of some kind.
Has this zone been quiet before and recently started hammering? If so, the likely culprit is your valve on that zone. Sprinkler valves are designed to close their valves relatively slowly in order to defeat water hammer caused by large quantities of water moving quickly and rapidly coming to a stop. Most major manufacturers of sprinkler valves have rebuild kits. Most valves can be disassembled in place so it means there is no changing of your system.
If this zone has always been hammering when shutting off, it is due to too large a volume of water having to suddenly stop when the valve closes. As stated in previous posts, the underground piping could be too small for the volume of water moving through it---very expensive fix, only a last resort.
An expansion chamber can be installed between the valve and your anti-siphon valve at the house. Its an inexpensive option and well worth a try.
You CAN change orifice sizes in your sprinkler heads so that they flow a smaller volume of water. It then makes your underground piping more sized to the zone requirements. This is a cheap fix and requires only a little effort from you. Once done, the timing on the zone would need to be increased as less water per minute is delivered after that change.
I had one zone behave like your on a previous system. It was quiet for 10 years before become a hammering situation. Rebuilding /replacing the valve "guts" was the solution that worked.
Good Luck and let us know how it turns out.
Someone PLEASE make me “water hammer arrestor for dummies diagram” I want to try and fix it this weekend.
Here’s what I’m working with
put one before the shutoff on the supply side ? Not after on the sprinkler side... It's just a T with a chamber... nothing fancy.
Or just put a vertical tube in this supply line? If so, what length?
Would that arrestor still work if I install it where the red arrow is pointing on the picture posted above?
yes, install the tee in place of the elbow as suggested. When the water rushes back it will go straight into the water hammer arrester. Do you have a shut off and pressure regulator below where the water comes out of the ground -that looks like the main water line. You really don't want say 90 - 120 PSI in your sprinkler system. No wonder it is hammering if that is the case.