Bonding screw stripped in panel
jhcrowman
Franklin, TN
Installing a new 200 amp service panel and when tightening the bonding screw on the neutral buss, the screw just spins and won't bite into the panel case. I guess I cranked down on it too much?
If I understand NEC 250.28 I should be able to add a bonding strap in its place, correct? see picture as an example.
I'm assuming I'd have to drill and tap either 8/32 or 10/32 depending on the screw size on the strap to get the correct number of threads in the metal case? Or would a self-tapping machine screw work just as well?
I'd appreciate any suggestions.
thanks!
rlitman
Long Island
If the screw is an 8-32, just run a 10-32 tap in the hole and buy a green 10-32 screw to put in its place.
sberry
Brethren, Michigan
No self drilling screws. I might say yes to a chunk of wire between bars. Put in ground bar which I like to do sometimes anyway depending on the style of panel. I added a bar to a panel job recently, it was so congested it let me take out a gob of wire and get the neutral spaces back I needed.
sparky 1971
Central Iowa
I had one strip out on me once. I just jumped a piece of #4 copper from the neutral bar to the ground bar. Do you still have a little piece left from the ground rods?
I would try pushing hard on the screw while turning it first. They are a ***** to get started sometimes. (post #4)
The panel isn't thick enough to use that screw. Two threads need to make contact with the panel. That is why there are the raised "*******" on the back wherever there are screws that go through it.
wyliesdiesels
Modesto, CA
are you using the same length screws as pictured? If so, it looks a little short since the neutral bar is on an insulating riser.
J
jhcrowman
Franklin, TN
I posted a picture on the first post - it shows as an attachment instead of an imbedded image.
I pushed hard on the screw while turning - it just gets to the point where it starts to feel tight and goes loose again. There's another panel right next to this one and I didn't have any problems tightening that bonding screw.
I'm pretty sure the screw is 10/32. I've opened a case with Siemens to see if their tech support has any suggestions.
I like the suggestion to run #4 solid between neutral bar and ground bar. 250.28 does say the bonding jumper shall be a "wire, bus, screw, or similar suitable conductor". That would be the easiest solution by far. I'll run that by the inspector to be sure he's okay with that.
thanks all!
bubinga
thanks all!
This is a Main Right?
sparky 1971
Central Iowa
thanks all!
I would just put the #4 jumper on and forget about it. If the inspector asks about it just tell him what happened. Otherwise, don't say a word.