Installing Two Panels in a Shop?
930dreamer
Amarillo,TX and Stinnett,TX
My shop currently has a messy 200 amp service, I'm in the process of replacing it. I also have a second 200 amp service that is live but not connect to anything( meter, disconnect, pole). If I ran wire for a second panel into the shop should the two panels be close to each other? I'd like to upgrade my three phase shop setup to 480v through a transformer. I currently have a 10hp rotary converter.
theoldwizard1
SE MI
Re: Installing Two Panel in a Shop?
My shop currently has a messy 200 amp service, I'm in the process of replacing it. I also have a second 200 amp service that is live but not connect to anything( meter, disconnect, pole). If I ran wire for a second panel into the shop should the two panels be close to each other? .
You are only allowed ONE feed to a building (with a few small exceptions).
Bert_
NW Iowa
You can have more than one panel. But they have to come from the same service and the disconnects must be grouped.
Norcal
Only 1 service to a building with limited exceptions, as already mentioned. Going to 480V is going to get expensive to do right.
wyliesdiesels
Modesto, CA
Only 1 feed allowed as has been said.
If you go the step-up transformer route, you will be paying to keep the transformer warm.
Have you asked your PoCo how much it would be to upgrade?
Bert_
NW Iowa
A 200A service should run a 10hp converter plus the rest of the shop just fine. Unless you have some other major loads your not telling us about.
I feel like you may have posted pictures in another thread but maybe you could post them again here along with your loads.
930dreamer
Yes, the current rpc will operate all the three phase machines I have. I plan to connect larger air compressor (15-20 hp) in the future. I'm sure the 200 amp will be fine, I pay a service fee on the other meter, better to have it and not need it........
theoldwizard1
SE MI
Disconnects ... like more than one ?
One feed, one (master) disconnect. A subpanel in the same building (at least residential) does not require a disconnect inside of that subpanel. Nice to have, but not required.
wyliesdiesels
Modesto, CA
NO youre thinking of the wrong thing. think of a multi-lug meter pan (not a meter main with a disconnect) with several disconnects coming off of it for feeds to several subpanels. The disconnects all need to be grouped in the same place.
Bert_
NW Iowa
Could have two service disconnects off the same meter. They would need to be grouped.
Common example is a 400A service feeding two 200A main panels.
Bert_
NW Iowa
If I build another shop I'll have it already.
If it powers nothing just have it shut off. Can always reconnect later. Why pay a monthly service charge?
Unless it doesn't meet current rules. Then the Poco won't hook it up until you correct it. They can't make you do anything if you keep the service active.
theoldwizard1
SE MI
Never dealt with a multi-lug meter pan. I am sure they exist, but a meter main sounds like a much better idea.
Sounds a lot like a meter main, except that the disconnects are not inside the same housing as the meter ! :bounce:
Bert_
NW Iowa
Don't all six need to be in the same panel?
Nope. Could be different boxes for each disconnect. They just need to be in the same area.
Even meter mains over 200A have more than one main. It's really pretty common. A 320A socket will always have lugs for multiple wires, or at least the option.
jeepxj
have you run into? what would the use case be?
1. Special conditions [225.30(A)]. These are:
• Fire pumps.
• Emergency systems.
• Legally required standby systems.
• Optional standby systems.
• Parallel power production systems.
and/or:
(E) Documented Switching Procedures. Additional feeders or branch circuits shall be permitted to supply installations under single management where documented safe switching procedures are established and maintained for disconnection."
dcg9381
Austin, TX
I thought there were new exceptions in the 2020 NEC that allowed dual-sourced buildings (no cite)?
I agree with jeepxj that prior versions of the NEC included "exceptions" - if the panels were grouped together and for special purposes, such as back-up power...
jeepxj
on the other hand: good luck getting the local inspector to tell you what documented safe procedures are for a residential application.
Norcal
The 2020 is only relevant if adopted by the State the OP lives in (Texas) and to my knowledge only Massachusetts has at this time.
jeepxj
Doesnt matter.
Having 2 power sources can be dangerous especially in a DIY setting.
Then why does the code include this? I'm not trolling; I agree single cut offs are ideal.
mike93lx
Richmond, VA
Documentation and procedures don't really align with at home DIY. That is really a commercial/industrial thing when you have electricians on staff
jeepxj
I agree to that. Is there something in the code that states it can't be used in residential applications?
mike93lx
Richmond, VA
well if we're gona cry code code code and then the code says something is allowed I'd like to at least understand a bit more. guess im doing some digging tonight.
Code is one thing. What battles you have to fight with your Ahj is another. The documentation and procedure wording is ambiguous enough that they could have an out saying it isn't up to snuff.