50 amp rv hookup at detached garage

gmtech

Well-known member
Joined
May 22, 2018
Messages
85
Location
nc
Looking to add a 50amp hookup near my detached garage for a camper. The garage feeder from house panel is 4 wire, and the ground/neutral are not tied together (didnt install the green screw)

Camper hookups are 4 wire, 2 hots, ground and neutral. The way I understand it, nothing actually uses 240 volts, just 2 seperate 120v, hence needing the neutral. Am I understanding this correctly?

I guess my question is, I should be able to just run a 4 wire feeder from garage to a pole at my camper with my 50amp recepticle and be good to go, right?

Thanks.






Sent from my SM-G973U using Tapatalk
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,614
Location
Richmond, VA
Yes.

Might be overkill, but throwing it out there. You can get boxes that give you your connection, plus an additional 30a rv or standard 20a 120v connection. Might be helpful to have a 120v outlet there in case you need to plug something in and the rv isn't there.

Here is one with 50a,30a and 20a outlets.

Your friend has shared a link to a Home Depot product they think you would be interested in seeing:

GE RV Panel with 50 Amp and 30 AMP RV Receptacles and a 20 Amp GFCI Receptacle
https://www.homedepot.com/p/GE-RV-P...a-20-Amp-GFCI-Receptacle-GE1LU532SS/203393689
 
OP
G

gmtech

Well-known member
Joined
May 22, 2018
Messages
85
Location
nc
Yes.

Might be overkill, but throwing it out there. You can get boxes that give you your connection, plus an additional 30a rv or standard 20a 120v connection. Might be helpful to have a 120v outlet there in case you need to plug something in and the rv isn't there.

Here is one with 50a,30a and 20a outlets.

Your friend has shared a link to a Home Depot product they think you would be interested in seeing:

GERV Panel with 50 Amp and 30 AMP RV Receptacles and a 20 Amp GFCI Receptacle
https://www.homedepot.com/p/GE-RV-P...a-20-Amp-GFCI-Receptacle-GE1LU532SS/203393689
I was planning to add a standard 20a recep, but this looks great. Once I get over the price, i may buy it lol Thanks.

Sent from my SM-G973U using Tapatalk
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,614
Location
Richmond, VA
Last edited:
To avoid these ads, REGISTER NOW!

chipdog4

Well-known member
Joined
Jul 14, 2016
Messages
481
Location
Southern Indiana
I was planning to add a standard 20a recep, but this looks great. Once I get over the price, i may buy it lol Thanks.

Sent from my SM-G973U using Tapatalk

They work pretty well

dscf3367.jpg
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,778
Location
Austin, TX
The way I understand it, nothing actually uses 240 volts, just 2 seperate 120v, hence needing the neutral. Am I understanding this correctly?

That's correct...

I guess my question is, I should be able to just run a 4 wire feeder from garage to a pole at my camper with my 50amp recepticle and be good to go, right?

Yes. I like the GE box above. I use Siemens Talon, same thing... Gives you 3 outlet types, 3 breakers, and GFCI.

Some of mine are actually wired 30A 240V. This powers 2 AC units on an RV just fine... And you can downgrade to 10GA copper wire (in most cases).
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I spose you could under wire the recept if it was current limited but really a good practice to wire recepts according to design, they worked out a whole approved system for this.
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,778
Location
Austin, TX
I spose you could under wire the recept if it was current limited but really a good practice to wire recepts according to design, they worked out a whole approved system for this.

Fair statement. I do label mine "30A". There's a big difference in 6GA and 10GA wire.. :)
 