230v 5HP Compressor Plug/Receptacle
atvkid4eva
Cleveland, OH
I just purchased a 230V 5hp Champion 80gal compressor. I currently have a 30 amp circuit ran with 10 guage wire. Can you guys recommend with plug/receptical would be best for this application? After some reading on here, some people say it needs to be hardwired due to no plug being rated for 5hp, but if possible i would prefer a plug. Let me know your thoughts. Thanks!
jdm5
CT
Well Properly rated pin and sleeve is fine too, but that will be big $$$. I found a used one on ebay for ~$100 for my install when I needed it.
A
atvkid4eva
Cleveland, OH
Yeah, I know this is an option as well. Could you give me anymore info on the type that you bought, so I could look into pricing.
Chuckster in NJ
Hunterdon County NJ
Check out Home Depot for a 250 volt/30 amp twist lock plug and cord cap then attach them to a piece of 10-3 SJO (rubber cord) and you will be good to go....... Very easy job!
BTW! There are plugs and receptacles available at HD for up to 50 amps.
matt_i
SE Michigan
Here's the thing. You can put a plug and receptacle, a L14-30 will do just fine, a 6-50 oven plug even better. It will run until the cows come home with no issues.
But then you don't get to stand under the roofline of the NEC.
The electrical code does have in mind arc-flash (if the plug is unseated with the motor drawing amps) which can damage you, the plug, and the receptacle which is why they spec hardwired for motor loads.
mike93lx
Richmond, VA
What is the advantage to a plug on a 5hp stationary compressor? Just trying to understand the goal.
A disconnect is code compliant and much cheaper.
mike93lx
Richmond, VA
Is your wire #10 in conduit or romex? If it is romex, 10/2 isn't enough for 5hp. You'll need either 8/2 romex or #10 thhn in conduit
Augus7us
Central Ohio
Per the sparkies here this is what I ran also (8/2). That and I thought that was overkill so I looked it up and, of course, the sparkies were correct.
My box is technically not in site of my breaker panel so I just have mine running to a disconnect then to my mag switch on my compressor. 5HP also for the record.
bradleykd
Georgetown, KY
I run mine on a 30A plug/socket. I am an electrician and understand the code, but I am willing to take to risk. Having an outlet allows you to use that 230V run for something other than the compressor if you have multiple things.
mike93lx
Richmond, VA
Whoops!! you are right, I just looked for "30 Amp" and didn't read the entire description. Does that mean any more than 3 HP draws more than 30 Amp?
No, a 5hp draws less than 30a when running.
If you unplug a motor when under load, it creates an arc flash hazard, which is very dangerous. Think super heated sparks. That's why high rated plugs are of a different style, called pin and sleeve where the prongs are shrouded
mike93lx
Richmond, VA
Is this "Arc flash" a real thing in the example we are talking about here ?
Please someone explain.
Marc
Google arc flash.
Yes, unplugging a motor under heavy load can cause one.
At high enough current and voltage, it can easily kill or seriously injure someone. Much more of an issue in industrial settings with 460V systems
7635tools
Southeast Wisconsin
If you’re an electrician, than you should have dedicated 240v outlets for your multiple things. Guys that aren’t in the know will do stuff like that but if you’re in the trade than you know better.
bob15
Northeasten, CT
Google arc flash.
yup.
As a side note, when I was traveling in India for work, the wall outlets all had a small switch that was to be thrown before unplugging anything, such the computer charging cord. If you didn't throw that switch there was a serious spark/flash. Crazy....
And India is 50hz, 230 vac
KhkSkQQkS_BtngB7GzfTglY0IC8KG-KiCSExh8XEg5onm50HkEQr1jY68ZVChu7_Y3s6IDXHWFMZnO3vjuYsSlgx6NFhZ6w
majerus
St. Louis Missouri
Put in a NEMA 14-50 and be done with it. That way if you get a welder, electric car or other high draw device you can support it.
mike93lx
Richmond, VA
Or just run a separate circuit for all of those, you know, the proper way.
Also none of of those actually require a 14-50
majerus
St. Louis Missouri
If an ev can pull 40 amps for 6 hours a compressor can run for 5 mins . I have been running my 5hp compressor and cadet heater on that plug. Of course I don't run both at same time and unplug them when switching between each. Going to large cannot hurt anything and it's one run that way instead of being limited in the future run it larger to begin with.
mike93lx
Richmond, VA
My point is that it is a 120/240 plug, which compressors, heaters and ev chargers don't need.
There is no question about a compressor being able to run with one. The issue is code prohibits it and it is unsafe if it is ever unplugged, intentionally or accidentally, when running.
But I'm glad you are happy with your setup
Viper98912
GA
Interesting read, learned a few things.
But a question - earlier in the thread it was stated that 10/2 wouldn't work for a 30 amp circuit and should be upped to 8g? How so?
brewchief
#10 nm-b is fine for a 30 amp circuit, the problem is motor circuits get sized via a table in the NEC and go by horsepower, IIRC a 5 hp motor requires wire rated for 35 amps, #10 thhn/ thwn in conduit would meet that or #8 nm-b.
Sent from my SM-T510 using Tapatalk
u3b3rg33k
you would probably be just fine with the CS63 non-NEMA connectors too, if you're going to do it anyways. those are shrouded and rated for disconnection under full load (not that it's a good practice).
Marc
ever see an arc welder, or plasma cutter in use? that's what will happen to your plug if you unhook it while the magic is happening.
A
atvkid4eva
Cleveland, OH
Lots of good info here! Thanks for all of that! So basically after reading through everything this is my conclusions...the current 30amp circuit has #10 nm-b wire. I can’t make out the words on the casing anymore, but I’m assuming it is not thhn because I don’t see a an insulator just a normal sleeve on the wire.. If this is true, I will need to replace this wire with #8 Nm-b since it is not run in conduit, but through the studs in the wall. I will leave the 30amp breaker in the sub panel? Or should I replace this with a 35amp breaker? I will then install a 30amp service shut off at the end of the new #8 Nm-b and hard wire the Compressor to that. Does this all sound correct and up to code? I want to do this the RIGHT way, I’d prefer not to burn my home shop down lol.
I also have another 50amp circuit in the shop, for a welder etc. so this would be dedicated to the compressor.
Also, what kind of wire would I run from the pressure switch to the 30amp shut off?
Thanks guys!
mike93lx
Richmond, VA
Thanks guys!
Thhn is individual conductors and must be run in conduit. The wires inside your nm-b are different.
Yes, change to 8/2 nm-b. You could run the 30a breaker or step up to a 40a (the next commonly available size.
From the disconnect to the comp, use a whip. Will either be flexible metal conduit or liquidtite. You'll need three pieces of 10 thhn for that (2 hots and a ground)
A
atvkid4eva
Cleveland, OH
Okay, yes that explains why thhn needs to be run in conduit. Thanks for the clarification.
And the 8/2 nm-b will be with ground? So two hots and a ground, correct? What is the reason I don’t need 8/3, why do I not need a neutral in this application?
brownbagg
its just the three prong welding maching plug, its rated for fifty amps so it be plenty
mike93lx
Richmond, VA
A neutral is only required when the device has a need for 120v, like controls on an oven. Your comp is 240v only