Lots of good info here! Thanks for all of that! So basically after reading through everything this is my conclusions...the current 30amp circuit has #10 nm-b wire. I can’t make out the words on the casing anymore, but I’m assuming it is not thhn because I don’t see a an insulator just a normal sleeve on the wire.. If this is true, I will need to replace this wire with #8 Nm-b since it is not run in conduit, but through the studs in the wall. I will leave the 30amp breaker in the sub panel? Or should I replace this with a 35amp breaker? I will then install a 30amp service shut off at the end of the new #8 Nm-b and hard wire the Compressor to that. Does this all sound correct and up to code? I want to do this the RIGHT way, I’d prefer not to burn my home shop down lol.
I also have another 50amp circuit in the shop, for a welder etc. so this would be dedicated to the compressor.
Also, what kind of wire would I run from the pressure switch to the 30amp shut off?
Thanks guys!