6 AWG vs 4 AWG
themiller
Seattle Suburbs
Which has a higher current carrying capacity - a 3’ run of copper 4 gauge or a 6” run of aluminum 6 gauge?
I think I know, just trying to confirm from an expert.
Thanks!
Bert_
NW Iowa
Current capacity has nothing to do with distance. Distance will affect voltage drop but doesn't need to be considered at that length.
Terry D
St. Louis, MO.
#4 copper is good for 85 amps
#6 Aluminum is good for 50 amps
Distance has nothing to do with how many amps can be put through a conductor.
What does determine how many amps can be put through a conductor is:
Size of the conductor
If the conductor is CU or AL
temperature rating of the conductor
Ambient air surrounding the conductor
How many conductors are in the raceway
If the load is a continuous load or not
u2slow
BC
Are we talking about insulation failure? ...or the wire turning to liquid?
Sounds more like a physics/engineering question than a Code question. :lol:
DenisG
Milwaukee
Pouillet's Law gives:
1.1823 milli-ohms for 3 ft of 6 AWG copper wire
2.0320 milli-ohms for 0.5 ft of 4 AWG aluminum wire
The copper wire (in this case) has lower resistance (better conductivity).
mike93lx
Richmond, VA
Oops! You're right ... recalculating ...
0.7455 milli-ohms for 3 ft of 4 AWG copper wire
0.3043 milli-ohms for 0.5 ft of 6 AWG aluminum wire
Aluminum wire (in this case) has lower resistance (better conductivity).
That is like the difference between 1000hp and 1010hp
They are effectively the same
kaffine
Henderson, NV
Ok how does 6 awg aluminum have less resistance than 4 awg aluminum? Looking at the answers in your 2 posts something isn't adding up.
PCustoms
VT
There's a huge difference in length between the 2 samples....
californiaHank
At 75°C, #6 Cu wire is about 0.491 Ohms per 1000 feet and #4 Al wire is about 0.508 Ohms per 1000 feet. (Source: NEC.)
Since they have about the same resistance per unit length, the NEC gives them the same maximum current ratings.
But, since the two runs are quite different lengths, the power losses are quite different:
3 feet of copper is roughly 3/1000 * 0.491 = approx 0.0015 Ohms
6 inches of aluminum is 0.5/1000 * 0.508 = approx 0.00025 Ohms
The losses in the (longer) copper run are about 6 times greater than in the (shorter) aluminum run.
wyliesdiesels
Modesto, CA
:+1: :rocker:
kaffine
Henderson, NV
More like 6 inches vs 36 inches...
Says 0.5ft in each. :dunno:
T
themiller
Seattle Suburbs
Thanks all - "current carrying capacity" was a poor choice of words.
I did review 310.15(b)(16), wanted to have my math and head checked was all. Appreciate it. This was more of an academic than a burn the house down type exercise.