6 AWG vs 4 AWG

themiller

Well-known member
Joined
Apr 24, 2012
Messages
4,805
Location
Seattle Suburbs
Which has a higher current carrying capacity - a 3’ run of copper 4 gauge or a 6” run of aluminum 6 gauge?

I think I know, just trying to confirm from an expert.

Thanks!
 
To avoid these ads, REGISTER NOW!

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,918
Location
NW Iowa
Current capacity has nothing to do with distance. Distance will affect voltage drop but doesn't need to be considered at that length.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
#4 copper is good for 85 amps

#6 Aluminum is good for 50 amps

Distance has nothing to do with how many amps can be put through a conductor.

What does determine how many amps can be put through a conductor is:

Size of the conductor

If the conductor is CU or AL

temperature rating of the conductor

Ambient air surrounding the conductor

How many conductors are in the raceway

If the load is a continuous load or not
 
Last edited:

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,647
Location
BC
Which has a higher current carrying capacity - a 3’ run of copper 4 gauge or a 6” run of aluminum 6 gauge?

I think I know, just trying to confirm from an expert.

Are we talking about insulation failure? ...or the wire turning to liquid?

Sounds more like a physics/engineering question than a Code question. :lol:
 

DenisG

Well-known member
Joined
Jul 14, 2013
Messages
1,278
Location
Milwaukee
Pouillet's Law gives:

1.1823 milli-ohms for 3 ft of 6 AWG copper wire
2.0320 milli-ohms for 0.5 ft of 4 AWG aluminum wire

The copper wire (in this case) has lower resistance (better conductivity).
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Oops! You're right ... recalculating ...

0.7455 milli-ohms for 3 ft of 4 AWG copper wire

0.3043 milli-ohms for 0.5 ft of 6 AWG aluminum wire

Aluminum wire (in this case) has lower resistance (better conductivity).

That is like the difference between 1000hp and 1010hp

They are effectively the same
 
To avoid these ads, REGISTER NOW!

kaffine

Well-known member
Joined
Dec 13, 2009
Messages
3,610
Location
Henderson, NV
Oops! You're right ... recalculating ...

0.7455 milli-ohms for 3 ft of 4 AWG copper wire

0.3043 milli-ohms for 0.5 ft of 6 AWG aluminum wire

Aluminum wire (in this case) has lower resistance (better conductivity).

Ok how does 6 awg aluminum have less resistance than 4 awg aluminum? Looking at the answers in your 2 posts something isn't adding up.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
Ok how does 6 awg aluminum have less resistance than 4 awg aluminum? Looking at the answers in your 2 posts something isn't adding up.

There's a huge difference in length between the 2 samples....
 

californiaHank

Well-known member
Joined
Nov 20, 2015
Messages
487
At 75°C, #6 Cu wire is about 0.491 Ohms per 1000 feet and #4 Al wire is about 0.508 Ohms per 1000 feet. (Source: NEC.)

Since they have about the same resistance per unit length, the NEC gives them the same maximum current ratings.
But, since the two runs are quite different lengths, the power losses are quite different:

3 feet of copper is roughly 3/1000 * 0.491 = approx 0.0015 Ohms
6 inches of aluminum is 0.5/1000 * 0.508 = approx 0.00025 Ohms

The losses in the (longer) copper run are about 6 times greater than in the (shorter) aluminum run.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,257
Location
Modesto, CA
#4 copper is good for 85 amps

#6 Aluminum is good for 50 amps

Distance has nothing to do with how many amps can be put through a conductor.

What does determine how many amps can be put through a conductor is:

Size of the conductor

If the conductor is CU or AL

temperature rating of the conductor

Ambient air surrounding the conductor

How many conductors are in the raceway

If the load is a continuous load or not

:+1: :rocker:
 

kaffine

Well-known member
Joined
Dec 13, 2009
Messages
3,610
Location
Henderson, NV
Pouillet's Law gives:

1.1823 milli-ohms for 3 ft of 6 AWG copper wire
2.0320 milli-ohms for 0.5 ft of 4 AWG aluminum wire

The copper wire (in this case) has lower resistance (better conductivity).

Oops! You're right ... recalculating ...

0.7455 milli-ohms for 3 ft of 4 AWG copper wire

0.3043 milli-ohms for 0.5 ft of 6 AWG aluminum wire

Aluminum wire (in this case) has lower resistance (better conductivity).

More like 6 inches vs 36 inches...

Says 0.5ft in each. :dunno:
 
OP
T

themiller

Well-known member
Joined
Apr 24, 2012
Messages
4,805
Location
Seattle Suburbs
Thanks all - "current carrying capacity" was a poor choice of words.

I did review 310.15(b)(16), wanted to have my math and head checked was all. Appreciate it. This was more of an academic than a burn the house down type exercise.
 