Hi all:

I'd like to run 200 amp service to a subpanel 150' from my meter. This will serve a detached guest house/bonus room. This subpanel will also provide power to my workshop.

The guest house will have a elec. water heater, oven, window A/C, septic ejector pump, fridge, and upright freezer. Shed will see normal tool stuff. Max draw would be 120v compressor and 30 amp welder. The guest/bonus room will be intermittent use initially but could transition to a full-time apartment later. The workshop is just hobby, so it is intermittent use.

I realize I might could get away with lesser service size (150 amp maybe) but would rather future-proof while I'm trenching and spending $$.

Can someone please double check my calculations that 2/0-2/0-2/0-#1 URD aluminum is OK for 200 amps direct bury at 150 ft?

(Disclaimer: I realize that this may present issues with my current drop service to house, but I will deal with upgrading to 320 amp or 400 amp service later if needed. Also I would rather not get a new drop service to the guest house.)

Any constructive input/suggestions are welcome!

Thanks so much!
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
2/0 Aluminum is rated at 135A. For 200A you need to use at least 250mil Al. I don't know how you got 2/0 Al is ok for 200A.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
I don't want to start a argument here or any big discussion, but here we are allowed to use 4/0 aluminum for service and subpanel feeders for dwelling units, and they consider that detached garage part of the dwelling. And I understand there are a lot of jurisdictions that don't allow using the dwelling table to size dwelling feeders, but there are some that do. But that's not figuring in any voltage drop. I would suggest to check with your local codes. But as already said, you cannot use 2/0 aluminum for 200 amp
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,962
Location
Richmond, VA
Besides gauge, URD can't go inside. You'll need to transition to something else before entering the building, if you are doing that.

Mobile home feeder can be run indoors (in conduit) plus direct bury

4/0 is good when it is feeding an entire primary structure, IIRC. In this case, it needs to be stepped up because it is going to a sub
 

Samh

Well-known member
Joined
Aug 16, 2006
Messages
482
Location
Canton GA
2/0 Aluminum is rated at 135A. For 200A you need to use at least 250mil Al. I don't know how you got 2/0 Al is ok for 200A.

Maybe he saw 2/0 CU, but I think that is even a little small for 200A. I just got 3/0 CU for my 200A
 
OP
D

-dirt-

Well-known member
Joined
Dec 27, 2011
Messages
58
The specs here listed 225 amps when direct bury for this cable:

https://www.wireandcableyourway.com/2-0-2-0-2-0-1-syracuse-underground-secondary-distribution-cable.html

Also, if I plugged the numbers in right, the Southwire Voltage Drop calc gave a 1/0 as acceptable for this scenario:

https://www.southwire.com/calculator-vdrop

I see where 2/0 is rated at 135 amps, but that's for one conductor, right? This has 2 plus the neutral and ground... Am I looking at this wrong?

https://images.homedepot-static.com/catalog/pdfImages/d2/d2013d0b-a2a0-4cc5-ba6d-d81edc5c9a50.pdf

Also, yes I'm aware URD needs to stay outside and that is no problem, as both panels (home and guest house) are exterior mounted. Will most likely stub up into a large junction box at the house and split bolt to smaller diameter copper for easier feeding into main breaker box.

Thanks for the help!
 
Last edited:

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
You can't go by what's listed on some resellers website, you need to follow the NEC. Also one conductor vs multiple conductors doesn't factor into the allowable ampacity. The max allowable amperage on a #2/0 Al conductor is 135A. You can pull 135A on one #2/0Al conductor @ 120V or 135A @ 240V on two #2/0Al conductors. With 240V the two conductors are 180deg apart so the amperage is switching between the two conductors.
 
Last edited:
To avoid these ads, REGISTER NOW!
OP
D

-dirt-

Well-known member
Joined
Dec 27, 2011
Messages
58
You can't go by what's listed on some resellers website, you need to follow the NEC. Also one conductor vs multiple conductors doesn't factor into the allowable ampacity. The max allowable amperage on a #2 Al conductor is 135A. You can pull 135A on one #2Al conductor @ 120V or 135A @ 240V on two #2Al conductors. With 240V the two conductors are 180deg apart so the amperage is switching between the two conductors.

Thanks for setting me straight! Straight forward responses with the reasoning behind them is why I really like this forum. :thumbup:
 
OP
D

-dirt-

Well-known member
Joined
Dec 27, 2011
Messages
58
If I go with individual conductors in conduit, is #6 copper ok for the ground between the panels? That looks right per Table 250.122...
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
If I go with individual conductors in conduit, is #6 copper ok for the ground between the panels? That looks right per Table 250.122...

Yes. Check with your local inspector to see if 4/0 Al is acceptablefor 200A, if so, then 4/0 MHF maybe your best option.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,089
Location
Modesto, CA
I don't want to start a argument here or any big discussion, but here we are allowed to use 4/0 aluminum for service and subpanel feeders for dwelling units, and they consider that detached garage part of the dwelling. And I understand there are a lot of jurisdictions that don't allow using the dwelling table to size dwelling feeders, but there are some that do. But that's not figuring in any voltage drop. I would suggest to check with your local codes. But as already said, you cannot use 2/0 aluminum for 200 amp

we can do that here too but ONLY when it is supplying the entire dwelling and nothing else.

he is also powering a shop with it.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
If the calculated load was 180A or less, 4/0 AL could be used for 200A.
 