LAN Cable In Feeder Conduit

zendriver

Well-known member
Joined
Dec 10, 2014
Messages
30,156
Location
Indiana
My electrical guy has run conduit for 100 amp feeder, to the garage and will finish next week..

I have not talked to him about it yet, but is it possible/problematic to include an Ethernet patch cable in the run?

Thinking I'd maybe just hard wire another router out there, verses just depending on WIFI.

Thanks
 
To avoid these ads, REGISTER NOW!

Zmann

Well-known member
Joined
Feb 24, 2019
Messages
302
Location
Arizona
I do not believe that is allowed but using the same trench is permissible , and they have direct burial cat 6 so it would be easy
 

Zmann

Well-known member
Joined
Feb 24, 2019
Messages
302
Location
Arizona
Matter of fact I may just run a data conduit in his trench and future proof for cameras/doorbell/alarm/flood sensor and other stuff you may be out of wifi range for
 
To avoid these ads, REGISTER NOW!

Don1357

Well-known member
Joined
Apr 15, 2019
Messages
948
Location
Palmer, AK
Most network cables are unshielded, the EMI from a feeder cable could mess transmission enough to render them incapable of passing data. Even shielded cables would have a hard time against the volumes of EMI a hot 100 amp cable can pass. Even if it was legal it would be a bad idea.
 

jdm5

Well-known member
Joined
Jan 1, 2012
Messages
281
Location
CT
It sounds like now is your chance! Put in 1 1/2 or 2” conduit for low voltage future use!
 

TuxThePenguin

Well-known member
Joined
Jul 8, 2020
Messages
633
Location
MA
Run a second conduit and/or use fiberoptic which is nonconductive (edit: only if you specifically buy fiber that is nonconductive) and legal to use in this manner (ethernet cable, having electrical conductors, is not legal to use in that manner). Personally I recommend using fiberoptic in a separate conduit (i.e. both options together).
 
Last edited:

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,665
Location
Long Island
Run a second conduit and/or use fiberoptic which is nonconductive and legal to use in this manner (ethernet cable, having electrical conductors, is not legal to use in that manner). Personally I recommend using fiberoptic in a separate conduit (i.e. both options together).

Not all fiber-optic cable is non-conductive. Many fiber-optic cables have metal inside to protect the fiber, and few of those have grounding means, so they are NOT all legal to run with electrical wires.
 

TuxThePenguin

Well-known member
Joined
Jul 8, 2020
Messages
633
Location
MA
Not all fiber-optic cable is non-conductive. Many fiber-optic cables have metal inside to protect the fiber, and few of those have grounding means, so they are NOT all legal to run with electrical wires.

good point
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,900
is the trench still open? drop a 3/4" pvc conduit run in there. you can share the trench. you cant share the conduit.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
I would oversize it a bit, 1” or maybe 1 1/4” due to current shortages of PVC it could be expensive to get crazy.
 