Ground routing in pole shed

Joined
Sep 6, 2015
Messages
7
Hey everyone, I’m currently having a 30x40 pole shed built and I am going to install a 100 amp sub panel in the building myself. I am planning on running 1/0-1/0-1/0-2 aluminum wire through a 2” conduit that will go through the concrete floor (floor not poured yet).

I’m going to install 2 ground rods outside the building and run #6 copper to those rods from the sub panel. One thing I’m not sure about though is how to get that copper wire from the box to the rods. Ideally I would run that wire in the same 2” pvc conduit as the feeder cable. I wound then pound the ground rods in the same trench as the feeder cable too. Are there any issues with doing that? My goal here is to run things through the floor to the outside so I don’t have any conduit showing above ground.
 
To avoid these ads, REGISTER NOW!

HeavyD1

Active member
Joined
Nov 10, 2014
Messages
25
Location
Michigan
I just did exactly what you are describing except I ran the ground adjacent to the feeder conduit, I put it through a small piece of conduit until I got to the bottom of the trench. Comes up next to the feeder conduit and will go right in the panel. Two rods in the trench.
 

bighouse01

Well-known member
Joined
May 21, 2009
Messages
293
Location
NY
If it's a sub panel it should have a 4 wire feed already,no need for extra rods.

I tried that. Got yelled at by the electrical inspector. Detached buildings/accessory building here in NY need their own rods. 8 feet long, 6 feet apart. I’m grounded at the garage and back to the house.....
 
OP
S
Joined
Sep 6, 2015
Messages
7
I just did exactly what you are describing except I ran the ground adjacent to the feeder conduit, I put it through a small piece of conduit until I got to the bottom of the trench. Comes up next to the feeder conduit and will go right in the panel. Two rods in the trench.

Did you run the smaller conduit all the way up to the box? Any chance you have some pics?
 

dmcintosh

Well-known member
Joined
Jul 24, 2013
Messages
250
Location
Smyrna, DE
When I built my pole building, I came through the floor with conduit to feed the panel as you've described, and then ran my ground rods 'inside' the building around the perimeter, leaving them high enough to still be exposed after the floor was finished. I didn't want to have the rods outside where they would be in the way. My inspector didn't say anything and I passed.

Where I may have gone astray, is that i did eventually finish my interior, so my grounding rods found themselves inside the wall cavity.
 
Last edited:
To avoid these ads, REGISTER NOW!

HeavyD1

Active member
Joined
Nov 10, 2014
Messages
25
Location
Michigan
Did you run the smaller conduit all the way up to the box? Any chance you have some pics?

I did not run the small conduit all the way to the box, just to get the ground through the floor. I have pics, but I am not able to figure out how to attach them because the site seems to want a link for a picture versus uploading.
 

HeavyD1

Active member
Joined
Nov 10, 2014
Messages
25
Location
Michigan
I think I figured out the picture thing, should be attached.
 

Attachments

  • Ground01.jpg
    Ground01.jpg
    131 KB · Views: 50
  • Ground02.jpg
    Ground02.jpg
    113 KB · Views: 44
  • Ground03.jpg
    Ground03.jpg
    119.5 KB · Views: 44

csp

Well-known member
Joined
Mar 23, 2010
Messages
5,719
Location
Franktown, CO
Why don't you just run your ground wire outside at the location where the panel is located?

Not sure why you'd want to run it through conduit just to get it to the same side the supply is coming in.
 
OP
S
Joined
Sep 6, 2015
Messages
7
Thanks everyone. After looking at it more I don’t think I’m going to run the ground wire in the feeder conduit. I will run it outside the conduit and exit the building.

I did install the feeder conduit today and the concrete is supposed to be poured on Tuesday. Since it will be going through the concrete floor I had to backfill around the conduit and the elbow where it turns horizontal. I can’t leave it uncovered until the rough-in inspection as that is a ways off. Will this be an issue with the inspector? The horizontal portion of the conduit is still visible in the trench outside the building but the portion under the building is obviously covered now.
 

HeavyD1

Active member
Joined
Nov 10, 2014
Messages
25
Location
Michigan
I don't know about your area, but I spoke to my inspector prior to filling in the trench and he was good with filling it in given that the floor needed to be poured before I could finish the electrical to the point of inspection. I did take plenty of pictures and my inspector was good with it when I explained it.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
31,963
Location
Coronado, CA
If your floor has not yet been poured, find out if you can use a UFER ground.
 
Last edited:

line guy

Active member
Joined
Nov 9, 2015
Messages
41
Location
upstate ny
a few pics. In new york 2 ground rods tied into ground bar in sub panel. #4 copper 1/2 conduit to go just outside barn.
 

Attachments

  • 20201203_130336.jpg
    20201203_130336.jpg
    93.5 KB · Views: 38
  • 20200412_131611.jpg
    20200412_131611.jpg
    128.4 KB · Views: 42

OneOfEm

Well-known member
Joined
Dec 7, 2015
Messages
255
Look up Ufer ground, for sure. It's done prior to the pour, so if it works in your area, now is the time.
 