Need some 200 amp meter base guidance

green.bubbly

Well-known member
Joined
Dec 14, 2008
Messages
2,156
Location
Lafayette, LA
BIL has an existing meter pole on his property that was used for his barn on his farm. All rusted and nasty and he wants to change it out to a new meter base panel combo. He also just pulled trailer home and wants to run 200amp service from that pole to the trailer. Trailer is about 30 feet from pole.

Looking at putting a Square D Homeline RC816F200C combo. This would give him a few circuits at the pole for his existing barn. We would then use a Homeline HOM2200BB 200 amp breaker to feed his trailer. Is this sound right? Breaker for this is almost 400 bucks from my quick search.


If this is a valid setup, will look.for a more affordable option for him..




https://www.homedepot.com/p/Square-D-Homeline-200-Amp-8-Space-16-Circuit-Outdoor-Ringless-Overhead-Underground-Main-Breaker-CSED-RC816F200C/100178340


https://www.gordonelectricsupply.com/p/Square-D-Hom2200Bb-Miniature-Circuit-Breaker-120-240V-200A-Requires-4-Spaces/5596803
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,004
Location
Modesto, CA
What does he have now? just a meter pan? or a meter main combo?

if just a meter pan, then the feed to the barn will need to be upgraded to 4-wire if it is not already.

does the trailer really need 200a?
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,718
Location
NW Iowa
Most of those meter/main panels have feed through lugs, you don't need another breaker. Don't buy anything until you figure out what is acceptable to your utility.
 
OP
G

green.bubbly

Well-known member
Joined
Dec 14, 2008
Messages
2,156
Location
Lafayette, LA
What does he have now? just a meter pan? or a meter main combo?

if just a meter pan, then the feed to the barn will need to be upgraded to 4-wire if it is not already.

does the trailer really need 200a?


He sent me a pic earlier. Just an old rusted out combo box. He plans on living in the trailer at some point. It looks like a large trailer.


Most of those meter/main panels have feed through lugs, you don't need another breaker. Don't buy anything until you figure out what is acceptable to your utility.


I was having trouble determining which home depot panels had the feed through lugs on their website. I will go to an electrical supply house on Thursday after getting info from the utility and get one that has the feed through lugs or the kit. All I know so far is that it is ring less meter base.


Thanks for the info.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,004
Location
Modesto, CA
He sent me a pic earlier. Just an old rusted out combo box. He plans on living in the trailer at some point. It looks like a large trailer.

I was having trouble determining which home depot panels had the feed through lugs on their website. I will go to an electrical supply house on Thursday after getting info from the utility and get one that has the feed through lugs or the kit. All I know so far is that it is ring less meter base.


Thanks for the info.

the part number you listed has feed thru lugs

see pg. 4

https://media.distributordatasoluti.../4c068a9e0bd4397900b6ac3ea3b6947377db381c.pdf
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,754
Does the trailer have gas appliances/heat? If so it is doubtful that it needs anymore then 100A, some of old double wides w/ gas only had 50A service.
 
OP
G

green.bubbly

Well-known member
Joined
Dec 14, 2008
Messages
2,156
Location
Lafayette, LA




:beer:



Does the trailer have gas appliances/heat? If so it is doubtful that it needs anymore then 100A, some of old double wides w/ gas only had 50A service.


It is all electric. He has "big" plans down the road. Outdoor kitchen slash workshop. RV hookup. Neither will ever happen unless poor thing hits the lottery.
 