Hello all,
Need some friendly advice here. Currently, I have a 5 hp Air Compressor in route, so I am gathering stuff for the electrical. The breaker box is in sight only 20ft away. The idea was to throw in either a 30amp/40amp breaker and 10/8 gauge wiring for the single phase. I'll know more once I read the motor.

Anyways, running 3/4 PVC from the Box, but can't decide if I should put a disconnect near the Compressor, or just use a gang for a junction. How do you have your electrical set up by compressor, and would you make any changes to how you have previously done it?
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,179
Location
Modesto, CA
If its a true 5HP motor, it will need to be hardwired with #10 THWN or #8/2 NM-b

Dont need a disconnect since panel is within 50’ unless its not within sight of the compressor
 
Last edited:

TRWham

Well-known member
Joined
Aug 11, 2017
Messages
2,004
Location
East Cobb County, Georgia
Happy with my current set-up. It runs in 3/4 EMT to the starter on the wall above and behind the compressor and in FMC from there to the terminal box. I do not have nor feel I need a separate disconnect as the circuit breaker serves that role. I do have a control switch that breaks the starter so we leave the circuit hot and just kill the control when it's not in use.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,854
Location
NW Iowa
When I wire 5hp motor it's normally #10 on conduit, 50A breaker. Might need a local disconnect if the panel isn't close.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,630
Location
BC
It runs in 3/4 EMT to the starter on the wall above and behind the compressor and in FMC from there to the terminal box. I do not have nor feel I need a separate disconnect as the circuit breaker serves that role. I do have a control switch that breaks the starter so we leave the circuit hot and just kill the control when it's not in use.

^ What I would do.

And check your compressor's owner's manual for other electrical particulars, like breaker sizing.
 
To avoid these ads, REGISTER NOW!
OP
R

RCrown

Member
Joined
Mar 22, 2021
Messages
5
Location
Camano Island, WA
Happy with my current set-up. It runs in 3/4 EMT to the starter on the wall above and behind the compressor and in FMC from there to the terminal box. I do not have nor feel I need a separate disconnect as the circuit breaker serves that role. I do have a control switch that breaks the starter so we leave the circuit hot and just kill the control when it's not in use.

I like that idea, eliminates going into the panel every time
 