I’m pretty sure what I found is not up to code, but I wanted to confirm before I swap breakers. Are there any exceptions to the code I’m not aware of? Or do 20 amp circuits always require 12ga wire?

Details:
Detached residential garage built in PA, USA in 2001. Dedicated lighting circuits with 20a breakers, 15a three way switches, 14ga neutral, 14ga travelers, 12ga power to the first switch. All THHN in PVC conduit. The total amount of lights per circuit draw less than 12 amps (80% of 15 amps), so I plan to switch out the 20a breakers for 15.
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Breaker is sized to the smallest amp rating wire used in the circuit. If 14 is used then breaker needs to be 15A.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,763
If it was a motor circuit, or A/C unit, it might be allowed, but for a branch circuit 14 AWG is 15A max.
 
To avoid these ads, REGISTER NOW!

NUTTSGT

Super Moderator
Staff member
Joined
Sep 14, 2009
Messages
50,998
Location
Northern Central Ohio
In a normal branch circuit, yes, 14 AWG should never have overcurrent protection exceeding 15 amperes.

We see it alot and when it gets cold for a week or so around 0°F, we see it in structure fires with electric heaters, knob/tube and 30A fuses.

Why 30A fuses, because they already blew the 20A fuses 2-3 times.
 

Metal-Marc

Well-known member
Joined
Aug 31, 2009
Messages
7,200
Location
Foothills of the Adirondacks
We see it alot and when it gets cold for a week or so around 0°F, we see it in structure fires with electric heaters, knob/tube and 30A fuses.



Why 30A fuses, because they already blew the 20A fuses 2-3 times.
I had an electrician replace the old main fuse panel with a modern breaker panel some 20 years ago. About one third of the fuse receptacles in the old panel were half melted.
 

TTTTTT

Well-known member
Joined
Jun 23, 2014
Messages
164
Location
Steenburg Lake, Ontario
So playing devils advocate here, if you added an led light off off a 20 amp circuit all wired with 12 gauge with a small piece of 14 gauge that would be a no no. The draw would be very small through that piece of 14. Obviously if the 14 gauge piece is in line and and continues to a 12 gauge that would a no
 
Last edited:

AntonLargiader

Well-known member
Joined
Nov 20, 2016
Messages
1,372
Location
Charlottesville, VA
Probably, but it seems to me the nature of the no-no would depend on the details. If you're plugging a 14g cord for the LED into a recep, you're just building a non-listed appliance assembly which many of us do all the time. If the 14g is part of the branch circuit, that's different.

So playing devils advocate here, if you added an led light off off a 20 amp circuit all wired with 12 gauge with a small piece of 14 gauge that would be a no no. The draw would be very small through that piece of 14. Obviously if the 14 gauge piece is in line and and continues to a 12 gauge that would a no
 

TTTTTT

Well-known member
Joined
Jun 23, 2014
Messages
164
Location
Steenburg Lake, Ontario
Thanks, I guess from a 20 amp 12 gauge fed junction box, you ran a single 14 /2 gauge wire to a switch to a led light from that junction box. Again a very small draw though the 14 gauge part.

Sent from my SM-T290 using Tapatalk
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,901
We see it alot and when it gets cold for a week or so around 0°F, we see it in structure fires with electric heaters, knob/tube and 30A fuses.

Why 30A fuses, because they already blew the 20A fuses 2-3 times.


when I bought my house, the two or three circuits supplying outlets on the main floor had been 'upgraded' to 50A breakers. 50A in 90 year old rubber covered 14AWG wire makes wire pretty crispy.
 