I’m pretty sure what I found is not up to code, but I wanted to confirm before I swap breakers. Are there any exceptions to the code I’m not aware of? Or do 20 amp circuits always require 12ga wire?
Details:
Detached residential garage built in PA, USA in 2001. Dedicated lighting circuits with 20a breakers, 15a three way switches, 14ga neutral, 14ga travelers, 12ga power to the first switch. All THHN in PVC conduit. The total amount of lights per circuit draw less than 12 amps (80% of 15 amps), so I plan to switch out the 20a breakers for 15.
Details:
Detached residential garage built in PA, USA in 2001. Dedicated lighting circuits with 20a breakers, 15a three way switches, 14ga neutral, 14ga travelers, 12ga power to the first switch. All THHN in PVC conduit. The total amount of lights per circuit draw less than 12 amps (80% of 15 amps), so I plan to switch out the 20a breakers for 15.