Getting ready to buy supplies for a workshop/shed. Plan is to run #2 AL, either MHF or XHHW, but I can't get conduit up to my main panel, so I need to switch to SER in my crawl space.
2018 code revision, in VA
#1 - junction box needs to be 6x conduit diameter, correct?
#2 - can I get away with 1.5" conduit? The run is short and simple (less than 30', 2 90 sweeps. I'd like to go straight into the back of the junction box on the other side of the house foundation from a LB.
I know that I'll hear 2" will be easier... A little harder pull doesn't bother me at all if it gets me a smaller junction box and smaller hole in the foundation.
Plan is to use Polaris connectors
In case it is mentioned, I will likely use a 60a breaker in the main (possibly up to a 90a but it depends on availability), with a 100a decent size panel in the shop, I'll pound in 2 ground rods with the right spacing and wire and the neutral bar will be unbonded
2018 code revision, in VA
#1 - junction box needs to be 6x conduit diameter, correct?
#2 - can I get away with 1.5" conduit? The run is short and simple (less than 30', 2 90 sweeps. I'd like to go straight into the back of the junction box on the other side of the house foundation from a LB.
I know that I'll hear 2" will be easier... A little harder pull doesn't bother me at all if it gets me a smaller junction box and smaller hole in the foundation.
Plan is to use Polaris connectors
In case it is mentioned, I will likely use a 60a breaker in the main (possibly up to a 90a but it depends on availability), with a 100a decent size panel in the shop, I'll pound in 2 ground rods with the right spacing and wire and the neutral bar will be unbonded