Only 24k for 1800sqft?

brianpgriset

Well-known member
Joined
Sep 29, 2006
Messages
1,043
Location
Beaumont, TX
I am ready to purchase a conventional split system for my shop building. Houston TX area. 30 x 60 x 14 eaves with 3/12 pitch. Wood frame, slab on grade building with steel PBR panel exterior. 3" closed cell foam on roof deck, 2" wall. I then finished out the stud bays with R13 fiberglass both roof and walls. The building uses 2x4 lath between the studs and steel exterior and the foam fills the void between the stud and steel so there is very little thermal bridging. 3 panel doors, all R18 insulated. No Windows. Very tightly sealed.

Everyone keeps telling me I need 3 tons minimum. But right now I just have a 70 pint dehumidifier in there and that alone actually makes it pretty decent.

I used the loadcalc.net calculator for load sizing. It doesn't have options for my construction type so I used assumed stucco/siding R13 with R6 foam board as a best approximation. I then entered in the wall and door surface areas. When I set outside temp to 95 and inside to 70 I'm getting only about 12kbtu heat load. Of that about 9000 is the doors and only about 2000 is the gain from walls. Lighting would add another 1600btu.

This would suggest I could cool the space with a very small system. I understand there are some varying loads like opening the doors, etc but I don't plan to pull hot cars in very often.

From what I see it's very common to oversize. I wanted to buy a 2 ton heat pump. Is this reasonable? Are my load calc numbers reasonable?

I figure, using the loadcalc numbers it'll take about 14000btu to keep the building at 70 with the lights on in the hotest days of the year. That would leave me 10000btu of spare capacity for dropping temps from high, appliances, etc.

I'd probably rather underside than oversize. But I'm curious if anyone else has a very very tight building similar to this.

Because the building is so tight I'd probably rather underside than oversize.
 
To avoid these ads, REGISTER NOW!

My Old Tools

Well-known member
Joined
Jun 4, 2014
Messages
5,438
Location
Hamrick Lake, TX
My building in east Texas is 30x40x12 with a 6/12 pitch, 22 feet to the peak. It has conventional roll insulation, 7 windows, man door and 12x12 overhead. I put in a 36k MrCool. It is pretty over sized by my estimation. It doesn't hurt anything as it throttles down, but I could have done a 24k easily I think. The first 2 days it ran hard and sucked a ton of moisture out. Once all the machinery stabilized to temperature, it just barely idles even on hot humid days.
 
OP
B

brianpgriset

Well-known member
Joined
Sep 29, 2006
Messages
1,043
Location
Beaumont, TX
I see why people like mini splits in this application but I really want a conventional split system for the ducting and filtration. Tough call for sure. Thanks for the data point.
 

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,410
Location
N CA
You can get filter boxes in woodworking stores, Rockler, Woodcraft, etc. I have a JDS that I run in my wood shop and it does an excellent job when combined with primary dust collection.
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,637
Location
Fargo, ND
I would recommend 3 ton also, but you ran the load calc on it!

One thing to consider, are you leaving the AC on all the time, or shutting it off and back on when you plan on working out there? If you re not leaving it on I would lean towards oversizing the unit. You don't want to turn it on at 100F outside and wait 2-3 hours for it to catch up.

My 24x38x9 foot garage will cool fine on 12,000 BTU if I let it run 24-7. Start it up when the shop was hot and it would never catch up, or at least until evening. When I put in central air I went with 1-1/2 tons and it works well.
 

kj_mustang

Well-known member
Joined
Feb 9, 2011
Messages
1,213
Location
Harrisonburg, VA
I have a 32 x 52 x 16 with spray foam and batts. I cool almost half of it with a 1.5 ton central a/c. It works great. I plan on doing a 2 ton package unit for the other half some day.
 
OP
B

brianpgriset

Well-known member
Joined
Sep 29, 2006
Messages
1,043
Location
Beaumont, TX
Thanks guys. My plan for use would be to keep it at high 70's on week nights then drop to low 70s on weekends. So somewhere between running all the time and only on weekends.
 

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
10,958
Location
Rhode Island
20,000 BTU keeps my 250-year-old poorly insulated ~1800 sq.ft house cool enough on a 95 deg day. For a modern, well-insulated building, the rule of thumb is generally around 1000 sq-ft/ton.
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,637
Location
Fargo, ND
Why does everyone continue to use "ton" as a measure? That is so 90's. It's BTU's this century.
Because it is a standard in the industry?

I have worked in HVAC for twenty years and "ton" is used all the time. Even manufacturers websites list equipment by tonnage.
 

BillK

Well-known member
Joined
Aug 24, 2006
Messages
9,322
Location
Beautiful Southern Maryland
Not sure how hot it is in Texas but . . . . the 30x60 x 15 h unit that my business is in has a 5 ton unit on the roof and the air handler hanging below it on the ceiling. The flat roof has about 6 inches of foam and I am in one of the center units so pretty well insulated on the sides. It was in the low 90's here today and it was running most of the day which is pretty normal. I keep it set at about 73. I do have a large parts spray washer that generates some heat but I keep it closed most of the time and it has a vent up through the roof. I cant imagine a 2 ton doing the job.
 

kelpaso1

MEMBER EMERITUS
Joined
Sep 28, 2009
Messages
3,962
Location
New Brunswick
Because it is a standard in the industry?

I have worked in HVAC for twenty years and "ton" is used all the time. Even manufacturers websites list equipment by tonnage.
Sorry, but standards change and you are behind on the terminology. BTU's is what we use these day's.
 

kelpaso1

MEMBER EMERITUS
Joined
Sep 28, 2009
Messages
3,962
Location
New Brunswick
1, 2 or 3 ton is irrelevant. It's BTU's in a system that matters as a whole. Building size, cooling/heating requirements etc.
 
OP
B

brianpgriset

Well-known member
Joined
Sep 29, 2006
Messages
1,043
Location
Beaumont, TX
What about something like this?


I honestly didnt know they made something like this. Seems like its best of both worlds.
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,637
Location
Fargo, ND

pizza

Well-known member
Joined
Dec 4, 2019
Messages
1,739
Location
Midwest, USA
Why does everyone continue to use "ton" as a measure? That is so 90's. It's BTU's this century.

on that note, why does everyone write BTU when they mean BTU/h?
BTU is a unit of heat, not power (heat per unit time). :)

"i drove 5 miles" vs "i'm driving 5 mph" -- different meaning.

1, 2 or 3 ton is irrelevant. It's BTU's in a system that matters as a whole. Building size, cooling/heating requirements etc.

what do you mean? it's not a different figure. both are units of heat rate (power).

1 ton of refrigeration = 12 kBTU/h
 
Last edited:

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,637
Location
Fargo, ND
What about something like this?


I honestly didnt know they made something like this. Seems like its best of both worlds.
Gree builds that unit for Mrcool. Nice unit. It comes in 2 to 3 TON and 4 to 5 TON.
Gree Flex
 
To avoid these ads, REGISTER NOW!

kelpaso1

MEMBER EMERITUS
Joined
Sep 28, 2009
Messages
3,962
Location
New Brunswick
what do you mean? it's not a different figure. both are units of heat rate (power).

1 ton of refrigeration = 12 kBTU/h

Must be a USA thing. Nobody in Canada uses the term "Ton". It's BTU's, which is the correct term. Do you use Ton for heating too?
 

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
10,958
Location
Rhode Island
BTU/h and Ton are equivalent. 1 Ton = 12,000 BTU. Heating is sometimes specified in tons. MBH (1,000s of BTU/h) is pretty typical for boilers and furnaces.

But if you really want to be pedantic, BTU/h is also an archaic standard, with most of the world simply using "watts" or "kilowatts".
 

pizza

Well-known member
Joined
Dec 4, 2019
Messages
1,739
Location
Midwest, USA
Do you use Ton for heating too?

probably not what you were asking, but i personally prefer to use SI (i calculate things in watts).

to actually answer your question, tons of refrigeration (TR) are just used to describe the power of cooling systems. that said, there's no reason you couldn't describe a heating system in TR since TR is just a unit of heat rate, but no one does. TR is old fashioned **** like horsepower. archaic but still used.

Wikipedia said:
The ton of refrigeration is equivalent to the consumption of one ton of ice per day and originated during the transition from stored natural ice to mechanical refrigeration.
 

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,048
I am ready to purchase a conventional split system for my shop building. Houston TX area. 30 x 60 x 14 eaves with 3/12 pitch. Wood frame, slab on grade building with steel PBR panel exterior. 3" closed cell foam on roof deck, 2" wall. I then finished out the stud bays with R13 fiberglass both roof and walls. The building uses 2x4 lath between the studs and steel exterior and the foam fills the void between the stud and steel so there is very little thermal bridging. 3 panel doors, all R18 insulated. No Windows. Very tightly sealed.

Everyone keeps telling me I need 3 tons minimum. But right now I just have a 70 pint dehumidifier in there and that alone actually makes it pretty decent.

I used the loadcalc.net calculator for load sizing. It doesn't have options for my construction type so I used assumed stucco/siding R13 with R6 foam board as a best approximation. I then entered in the wall and door surface areas. When I set outside temp to 95 and inside to 70 I'm getting only about 12kbtu heat load. Of that about 9000 is the doors and only about 2000 is the gain from walls. Lighting would add another 1600btu.

This would suggest I could cool the space with a very small system. I understand there are some varying loads like opening the doors, etc but I don't plan to pull hot cars in very often.

From what I see it's very common to oversize. I wanted to buy a 2 ton heat pump. Is this reasonable? Are my load calc numbers reasonable?

I figure, using the loadcalc numbers it'll take about 14000btu to keep the building at 70 with the lights on in the hotest days of the year. That would leave me 10000btu of spare capacity for dropping temps from high, appliances, etc.

I'd probably rather underside than oversize. But I'm curious if anyone else has a very very tight building similar to this.

Because the building is so tight I'd probably rather underside than oversize.
your dehumidifier ADDS heat(temperature) to the space, so if it's running and not a furnace in there yeah you are likely fine.

FYI: a typical 3 ton 2 stage is 1.98 tons on stage 1. you can have both.

or you could get something like a 3T ODU bosch bova 2.0 system and just pick an airflow target, and let the ODU adjust it's RPMs to match your load. it's basically a minisplit in traditional clothing meant for regular thermostats.
 
OP
B

brianpgriset

Well-known member
Joined
Sep 29, 2006
Messages
1,043
Location
Beaumont, TX
Purchased the Mr Cool universal split today from Ingrams. Seems like the best of both worlds; variable output, high efficiency, conventional air handler, and DIY friendly.

Only drawback was it cost a few hundred more than a comparable traditional split heat pump but im willing to sacrifice that for the benefits.

We'll see how it goes.
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,761
Location
Austin, TX
I have 48,000 BTU of mini split cooling a 40x60x16 in central Texas. Open cell foam all the way around, maybe R-12 - R-15. 3 huge crappy insulated doors.
Nice thing about mini-splits is you can always add another.. :)
 

Yankeefarmer

Well-known member
Joined
Jul 25, 2011
Messages
1,184
Location
Connecticut
Purchased the Mr Cool universal split today from Ingrams. Seems like the best of both worlds; variable output, high efficiency, conventional air handler, and DIY friendly.

Only drawback was it cost a few hundred more than a comparable traditional split heat pump but im willing to sacrifice that for the benefits.

We'll see how it goes.
I think you’ll be happy with it. I installed the 4-5 ton model (based on heating needs) and am very satisfied. Just yesterday I saw a video from Ingram’s affirming that the warranty is valid with a DIY installation if you use their precharged line set.
 

Selkirk

Active member
Joined
Jul 30, 2009
Messages
37
Location
Houston/Matagorda TX
Purchased the Mr Cool universal split today from Ingrams. Seems like the best of both worlds; variable output, high efficiency, conventional air handler, and DIY friendly.

Only drawback was it cost a few hundred more than a comparable traditional split heat pump but im willing to sacrifice that for the benefits.

We'll see how it goes.
Please keep us posted on how the install goes, and you thoughts on the Mr Cool universal quality. I have a weekend place that needs a new split system, Mr Cool universal and maybe Bosch heat pump split are on my short list.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,729
Location
NW Iowa
Why do you guys keep saying "tons"? Mini splits are rated in BTU's (at least up here). I don't care if 1 ton equals whatever BTU's. Use the correct terminology.
Why do you keep talking about BTU. Down here the standard is "ton".

If I talk to my wholesaler and ask for 30,000 btu he's going to say "how many ton is that?"
 

kelpaso1

MEMBER EMERITUS
Joined
Sep 28, 2009
Messages
3,962
Location
New Brunswick
Why do you keep talking about BTU. Down here the standard is "ton".

If I talk to my wholesaler and ask for 30,000 btu he's going to say "how many ton is that?"
Opposite can be said here. I could ask for a 3 ton unit and they will ask how many BTU's?
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,729
Location
NW Iowa
Opposite can be said here. I could ask for a 3 ton unit and they will ask how many BTU's?
That just went right over your head...

Nobody else in this thread is going to talk to a supplier in Canada. In this thread it doesn't matter what unit of measure you use... It's that simple
 

Trock03

Well-known member
Joined
Jun 16, 2014
Messages
125
Location
West of Houston
Hey OP I'm in the Houston area and an curious to know how this works out for you so please let us know how it goes. Knowing your results might help me out a TON on my project.

kelpaso1 - I hope my use of ton didn't offend you. Enjoy your BTUs and your round bacon.

TC
 