I am about to wire my new detached garage/shop. If it matters, it cannot and will not be able to be used as a dwelling structure. My state of TN uses NEC 2017.
210.52(G)(1) Garages- In each attached garage and in each detached garage with electric power, at least one receptacle outlet shall be installed in each vehicle bay and not more than 1.7 m (5 ½ ft) above the floor.
210.11(C)(4) Garage Branch Circuits. In addition to the number of branch circuits required by other parts of this section, at least one 120-volt, 20-ampere branch circuit shall be installed to supply receptacle outlets in attached garages and in detached garages with electric power. This circuit shall have no other outlets. Exception: This circuit shall be permitted to supply readily accessible outdoor receptacle outlets.
I am confused a little. I am planning on many more than 2 outlets. I had assumed my 20- 2 gang boxes would be plenty and far exceed minimum requirements. Now I am wondering if they are saying I must put those 2 outlets on their own dedicated branch circuit.
Next just to be sure- They are saying I can put my two outside outlets on the same circuit with the garage bay outlets. Correct?
I have other questions. These are good starters.
210.52(G)(1) Garages- In each attached garage and in each detached garage with electric power, at least one receptacle outlet shall be installed in each vehicle bay and not more than 1.7 m (5 ½ ft) above the floor.
210.11(C)(4) Garage Branch Circuits. In addition to the number of branch circuits required by other parts of this section, at least one 120-volt, 20-ampere branch circuit shall be installed to supply receptacle outlets in attached garages and in detached garages with electric power. This circuit shall have no other outlets. Exception: This circuit shall be permitted to supply readily accessible outdoor receptacle outlets.
I am confused a little. I am planning on many more than 2 outlets. I had assumed my 20- 2 gang boxes would be plenty and far exceed minimum requirements. Now I am wondering if they are saying I must put those 2 outlets on their own dedicated branch circuit.
Next just to be sure- They are saying I can put my two outside outlets on the same circuit with the garage bay outlets. Correct?
I have other questions. These are good starters.