Question on sub-panel for new shop
JoeEngler
I have seen a lot of questions on sub panels for remote shops. I just wanted to put all my information and see if my planning is correct. First the building will be a metal building.
  • The building is about 45 feet from the house.
  • The plan is to run (3) #4 wires and (1) #6 for ground
  • 2 Grounding rods that will be placed at least 6 feet apart.
  • 60- or 70-amp breaker in the house to feed the sub-panel
  • Currently it looks like it will (4) 110v breakers and (3) 220v breakers
  • 3 - 20 amp for outlets (110v)
  • 1 – 15 amp for lighting (110)
  • 1 – 20 amp for air compressor (220v)
  • 1 – 25 amp for mini spilt (220v)
  • 1 – 30 amp for welder (220)
Now for the big question, I bought a square-d sub panel that is MLO 86428. However, after reading several posts, it seems that I need a disconnect in the garage. I think my choices are going to be.
  • Add a main breaker to the purchased panel
  • Back feed a breaker with a hold down
  • Return the panel and buy one with a main breaker
  • Install a separate disconnect.
If I use a main breaker, I have heard it should be a higher amperage then the breaker in the house. The logic I read was that this would make sure the breaker in the house stays the breaker and the one in the garage at a higher amperage would not trip is this correct?
Sorry if I’m asking the same question someone else may have. I have searched a lot a just want to make sure it is correct and not have to have the inspector come back several times and burn more money.
sparky 1971
Central Iowa
The easiest, most cost effective thing is going to be return the panel and buy a 100 amp main breaker panel. Don't worry about the fact that it's 100 amp, it's just a disconnect. The breaker in the house is your ocp.
pattenp
Virginia - USA
For a 60 to 70 amp feeder breaker, #6cu thhn in conduit is sufficient. 60A only needs a #10cu egc, 70A will be #8cu egc. But, nothing wrong with the sizes you stated.
J
JoeEngler
For a 60 to 70 amp feeder breaker, #6cu thhn in conduit is sufficient. 60A only needs a #8 egc, 70A will be #6 egc. But, nothing wrong with the sizes you stated.
Thanks, if I stay with #4 I could use a 90A breaker in the house or use #6 and keep it at 70A?
J
JoeEngler
Seems like the logical thing to do. I will return and buy the panel with the 100A main breaker
yatg
Southern Oregon
You've already filled up 10 slots of the 12 slot panel you speced.
Doesn't leave much room for expansion.
For $99 you can get a main panel, 30 slots, and it includes a few breakers you can use.
Terry D
St. Louis, MO.
For a 60 amp circuit, #10 copper is good for the EGC. A 70 amp circuit, #8 copper is good for the EGC. The sizes you posted is for aluminum.