50 feet Cobblerhow long of a run do you plan to want, you need at least #8
Yup. It's pretty old Wyliethats an old spider box. the 50a receptacle is an old style NEMA 10-50 3 prong non grounded 125/250v. you should replace it with a 14-50 4 prong receptacle but the physical size wont be the same.
Actually I think it is groundedthats an old spider box. the 50a receptacle is an old style NEMA 10-50 3 prong non grounded 125/250v. you should replace it with a 14-50 4 prong receptacle but the physical size wont be the same.
aww i missed that 4th prongActually I think it is grounded
Looks like this type of connector is needed and it says it's 4-wire
I believe ground is on the side- see green arrow
That's the one. Those are pretty common on those spider boxes.Actually I think it is grounded
Looks like this type of connector is needed and it says it's 4-wire
I believe ground is on the side- see green arrow
Along with the case the pin in the center is also a ground.Actually I think it is grounded
Looks like this type of connector is needed and it says it's 4-wire
I believe ground is on the side- see green arrow