50 amp contractor extension cord locking connectors

1190R

Well-known member
Joined
Jul 31, 2014
Messages
252
A friend gave me a spider box for power distribution
I would like to buy an outdoor rated 50 amp extension cord with the correct locking connector
What type of connector and what gauge wire should I be looking for?
 

Attachments

  • Spider box 2.png
    Spider box 2.png
    2 MB · Views: 54
  • Spider box 1.png
    Spider box 1.png
    1.9 MB · Views: 54
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,022
Location
Modesto, CA
thats an old spider box. the 50a receptacle is an old style NEMA 10-50 3 prong non grounded 125/250v. you should replace it with a 14-50 4 prong receptacle but the physical size wont be the same.
 
OP
1

1190R

Well-known member
Joined
Jul 31, 2014
Messages
252
thats an old spider box. the 50a receptacle is an old style NEMA 10-50 3 prong non grounded 125/250v. you should replace it with a 14-50 4 prong receptacle but the physical size wont be the same.
Yup. It's pretty old Wylie
Are you saying I'm going to have to modify the metal box?
 
OP
1

1190R

Well-known member
Joined
Jul 31, 2014
Messages
252
thats an old spider box. the 50a receptacle is an old style NEMA 10-50 3 prong non grounded 125/250v. you should replace it with a 14-50 4 prong receptacle but the physical size wont be the same.
Actually I think it is grounded
Looks like this type of connector is needed and it says it's 4-wire
I believe ground is on the side- see green arrow
 

Attachments

  • Hubbell2.png
    Hubbell2.png
    228 KB · Views: 47
To avoid these ads, REGISTER NOW!

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
31,961
Location
Coronado, CA
I would take the box to a good Wholesale house and buy the appropriate connectors and #6 AWG cable. You could get by with #8, but 6 gives you a greater margin of safety.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,022
Location
Modesto, CA

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,742
Location
NW Iowa
Actually I think it is grounded
Looks like this type of connector is needed and it says it's 4-wire
I believe ground is on the side- see green arrow
That's the one. Those are pretty common on those spider boxes.
 