Well-known member
Skip to the pictures for the carnage.....come back up for the story if interested.
House was built 6 years ago and the pool was done at the same time. Fast forward to this week and every time the heater (Pentair UtlraTemp 110 heat pump) runs, it pops a breaker after about 5 hours of running, sometimes longer. I call the Pentair tech out. All the equipment checks out - capacitor is good, amp draw when running is within spec. I tell him it's strange that the whole thing runs for hours, but throws a breaker after the heat has been on a while - maybe a loose connection somewhere. He checks a few connections at the breakers and all looks tight.....We now have the most maddening of problems: intermittent and difficult to reproduce.
The tech says he has to pass it off to the electrician. No problem. This morning I have another look at the whole pad and wall, and think to myself that there's no way they shoved all those wires into this little plastic box - and why would they to begin with. Shouldn't this have been a straight shot from the pool pad breaker panel to the main in the garage? So I remove the cover off this 4" box.....looks like a damn car fire in there. Three of the four wires compromised. One of the hot wires baked all the way open and half the copper strands broken and splayed out. The pictures tell the tale.
I begin to triage and consider how to fix this - it's Florida hot, we leave town in four days, the dog is running around with a post-op cone on its head, and I gotta go back to work tomorrow. As I noodle the details, the wife finds an electrician (known, legit local outfit) who will be here in 1/2 an hour. The guy's eyes open wide when he sees the carnage. After assessing it, he tells me that a 60 amp breaker feeding 4 gauge wires (about a 100' run) is too small for a combination of the pool pump, heat pump, the blower for the hot tub, and whatever it takes to the electronics board and valves. But it ran for almost 6 years? He tells me undersized wiring, cycling on and off, with that load over the years took its toll.
Cramming all those wires in this little box can't be correct.....I don't know about the 4 gauge over that distance with that load. The electrician says it would be correct if the pool was heated with gas instead of a heat pump. The wife is uninterested in the several days I would spend pondering, solving, fixing, etc.....She wants it done pronto. What do they say, "good, fast, cheap.....pick two?" Running new wire, upgrading to 2 gauge from the main in the garage through the attic and whatever else needs to be done: I'll take good and fast for $4600.00. Ouch.





House was built 6 years ago and the pool was done at the same time. Fast forward to this week and every time the heater (Pentair UtlraTemp 110 heat pump) runs, it pops a breaker after about 5 hours of running, sometimes longer. I call the Pentair tech out. All the equipment checks out - capacitor is good, amp draw when running is within spec. I tell him it's strange that the whole thing runs for hours, but throws a breaker after the heat has been on a while - maybe a loose connection somewhere. He checks a few connections at the breakers and all looks tight.....We now have the most maddening of problems: intermittent and difficult to reproduce.
The tech says he has to pass it off to the electrician. No problem. This morning I have another look at the whole pad and wall, and think to myself that there's no way they shoved all those wires into this little plastic box - and why would they to begin with. Shouldn't this have been a straight shot from the pool pad breaker panel to the main in the garage? So I remove the cover off this 4" box.....looks like a damn car fire in there. Three of the four wires compromised. One of the hot wires baked all the way open and half the copper strands broken and splayed out. The pictures tell the tale.
I begin to triage and consider how to fix this - it's Florida hot, we leave town in four days, the dog is running around with a post-op cone on its head, and I gotta go back to work tomorrow. As I noodle the details, the wife finds an electrician (known, legit local outfit) who will be here in 1/2 an hour. The guy's eyes open wide when he sees the carnage. After assessing it, he tells me that a 60 amp breaker feeding 4 gauge wires (about a 100' run) is too small for a combination of the pool pump, heat pump, the blower for the hot tub, and whatever it takes to the electronics board and valves. But it ran for almost 6 years? He tells me undersized wiring, cycling on and off, with that load over the years took its toll.
Cramming all those wires in this little box can't be correct.....I don't know about the 4 gauge over that distance with that load. The electrician says it would be correct if the pool was heated with gas instead of a heat pump. The wife is uninterested in the several days I would spend pondering, solving, fixing, etc.....She wants it done pronto. What do they say, "good, fast, cheap.....pick two?" Running new wire, upgrading to 2 gauge from the main in the garage through the attic and whatever else needs to be done: I'll take good and fast for $4600.00. Ouch.