Compressor to Generator Plug?
D45
NW INDIANA
Trying to help a neighbor out
The attached pic of the plug for the cord on his compressor
He wants to be able to run the compressor off his generator
He told me the compressor was 240v
Any idea what type of plug this is and how can he run the compressor off the generator?
Is there an adapter plug.or doss he need a new plug end?
mike93lx
Richmond, VA
That is a Nema 6-20p and it is 240v. You would need to make or buy an adaptor to the L14-30R on that panel.
Depending on the surge rating of that generator and the HP rating of the compressor, it may have a hard time starting
D
D45
NW INDIANA
Thanks!!!
I found a few adapters for these two plug connections on ebay and Amazon
Wrench97
Southeastern Pa
Just because you found a adapter does not mean it will work, what is the amp rating on the compressor motor's tag?
mike93lx
Richmond, VA
You are also plugging a 20a device into a circuit rated higher.
Sometimes we do what we have to in order to get something done, but if this is a long term solution, it's not the best way to do it
D
D45
NW INDIANA
Motor decal says
13.1 amps
230v
matt_i
SE Michigan
The back-emf aka "inrush" on starting an AC motor can cause the generator to not be able to handle the amp load.
The 13.1A is likely a steady state max amperage (full load amps or FLA) at max HP.
Not uncommon to double the FLA when starting, its just a spike but needs to be overcome.