Recent content by Black Oak

  1. B

    Single zone Mini split for 40x48 barn

    Quote Folks have pointed out to me which brands are made by the same manufacturer , and most believe Pioneer ,Blueridge .and Senville to be close to the same units . Rebadged but all pretty much the same . IF true , Senville will be the lowest cost , based on what is included or not - based on...
  2. B

    MrCool or Ramsond or.. ? Multi-zone?

    Pioneer , Blueridge , Senville , and Mr. Cool( I believe) are all made by the same company in China . Senville however includes all the lineset and pcs. to install . If looking at those choices , Senville saves a little money .
  3. B

    Question on insulating 24x36x12 pole barn

    where do you live ?
  4. B

    Mini split installation

    " Generally Speaking " , mini split mfgrs. tell you 10' minimum =25' max . Above 25' length you need to add some refrigerant , not something all that simple to do correctly . I'd locate the outdoor unit where it allows this issue to go away if possible . My last one was 41 ft.- I had a pro add...
  5. B

    HVAC for Retirement Shop Upgrade

    The initial heating of the slab is the most costly , maintaining that level is less costly .It's t he on / off , up / down that kills you . True of both radiant and mini splits .
  6. B

    HVAC for Retirement Shop Upgrade

    I'd seriously consider Radiant Floor heat in the new floor . There is no comparison to forced air . Mini splits are great for AC , but will struggle in the coldest months . Do some research on radiant heat .
  7. B

    Need to add R410A to my Mini Split . Got some questions .

    Male to male fittings and Nylog were used . This was a unique install - 100 yr. old log cabin structure w/ special circumstances . I would have liked to go with a one piece line set , but going with 2 line sets combined was really the only option on this old house . Yes , gauges were used ...
  8. B

    Need to add R410A to my Mini Split . Got some questions .

    Thanks . Yes , I released the vacuum after 24 hrs. , install is in a few days . I also found the refrigerant table in the manual , it doesn't call for that much .
  9. B

    Need to add R410A to my Mini Split . Got some questions .

    This is my fourth mini split install , this one is a Senville 24,000 btu . This is the first time the line set is over 25 ft. - its 41 ft . It is in place and holds a vacuum fine . 5/8" and 3/8" tubing . I have a pro HVAC man willing to add the R410A ( my buddy's boss ) . I'd like to know...
  10. B

    Looking for exterior foam insulation and UV stable sleeve for minisplit

    look at pipe insulation commonly used on water lines under the house etc.. I've found 3" I.D. at the big box store .
  11. B

    Mini Split Line Set Size

    I have no first hand , solid info for you . I do think you must use the required larger tubing or your headed for bad performance/ problems down the road . I'm sure you'll have an answer pretty quick .
  12. B

    New Garage build In NW Arkansas and insulation

    I'm in NE Ark. , and don't think 24K is enough . If this is a pole barn , 14' walls is almost double what a load calc. is using to give "sizing" guidelines - lots of sq. ft. You'll get your best results eliminating all air infiltration possible . How about rigid foam between the girts...
  13. B

    Metal Building AC Sizing 40x40 TX

    I'd consider more insulation if it's not too late . Add some batts in some fashion . A metal building in Texas is going to be a challenge to keep cool .
  14. B

    Radiant Heat in Shop/did I do it right?

    I've read " keep your loops or runs under 300 ft. , try to keep them equal in length " . OP said 500 ft. runs - he has colder fluid coming back to the boiler than is optimum .