  1. D

    Unit Heater size

    Natural gas is now to the new building. I will be in the building during winter only occasionally. I read some posts about radiant tube heaters on this site. Based upon needing to quickly bring temps up from 40 degrees to 70 degrees, I understood that unit gas heaters were recommended over...
  2. D

    Unit Heater size

    You are correct in your assumptions. I'm just a guy that wanted some help. The gas line and shut off valve have already been run to the new building by a professional. I just thought that I was capable of hanging a unit from the ceiling with threaded rod.
  3. D

    Unit Heater size

    Thank you. I am not experienced in these matters and had no clue on what size heater to buy. Is there any other information that I could provide that would be helpful to assist with a recommendation from someone more knowledgeable than myself?
  4. D

    Unit Heater size

    Jvitez: Thank you for the very useful information. I need the help as I am not experienced in sizing the unit. After reading your post I started researching 75 Btu units. The technical details state "up to 950 sq ft with 7-8 ft ceiling height." My ceiling height is 12'3" and as you computed I...
  5. D

    Unit Heater size

    OK, I did a search and read a lot of posts. Still confused on size. From what I have read, you can oversize. I am thinking about a 75 BTU or 100 BTU. New post construction with steel interior walls and ceiling. R19 in walls and R30 in ceiling. Building is 28x48 with 12' ceiling. Location...
  6. D

    Gas unit heater - installation height?

    Already getting some good feedback. Thank you and keep the replies coming. As you can tell, I'm not too experienced. Additional info: I do plan to vent out the side wall. Thanks for the tip on ceiling fans, sounds like a good idea. Can you really just use an eye lag bolt into the 2x4 truss...
  7. D

    Gas unit heater - installation height?

    New post frame construction building is 28'x48'x12. Walls at R19 and ceiling at R30. Interior walls and ceiling finished in steel. Indiana location. I'm thinking that a 100 BTU natural gas unit heater will do. How far down from the 12' ceiling should I hang the unit?