  1. G

    Modine Hot Dawg heater smell

    Is it a brand new heater? If so, there is an oil coating on the heat exchanger that should be burned off on start up with the windows open. If it's an old heater, I would check the flue and heat exchanger for holes/cracks. Otherwise it could be another source in the apartment making those fumes.
  2. G

    Can i use Double wall Cat 3 piping for horizontal install?

    Big Maxx heaters have a section in the install manual on horizontal venting requirements. Code typically refers to manufacturer instructions for vent categories other than type 1. Mr Heater states the heater is rated for cat 3 vent pipe in horizontal configurations, so you need to use stainless...
  3. G

    Can i use Double wall Cat 3 piping for horizontal install?

    Horizontal install must be stainless steel. Double wall galvanized is called B vent, which is not permissible in most locations for horizontal installs.
  4. G

    Specific thermostat requirements

    I don't know of any standard residential thermostat that could do that, maybe someone else does. Might be easier to wire a timer on to the heater and program it for what you want. Just leave the thermostat in heat mode, then when the timer allows, will pass power or signal to the heater.
  5. G

    Baseboards still hot, new thermostats tuned off

    I'm a bit confused, do you have a boiler or forced air furnace? I'm assuming a boiler based on you saying you have baseboards. Do you have zone valves or circulators? You might be getting backflow from your lower zone to your upper zone and due to lack of check valves on either the circulators...
  6. G

    Common Venting

    Common venting won't work with what you currently have. Is there a particular reason you want it common vented?
  7. G

    Where can you add a “C” wire on a Becan/Morris garage heater model TBUF- BR075?

    Tie the common wire on to the 24v transformer secondary "white" wire.
  8. G

    Mr. Heater 4" Appliance Adapter

    Single wall clearance to combustibles is generally 6 inches. Clearance to combustibles can be reduced with proper barrier materials but I think you'll have to blast a new hole to make it right. Thimble appears to be the wrong type, doesn't have proper clearance around the circumference.
  9. G

    Mr. Heater 4" Appliance Adapter

    Vertical allows for B vent provided your horizontal run is 75 percent or less than the vertical portion. So if you have 10 feet of vertical rise, and your horizontal is less than 7.5 feet, you can use B vent.
  10. G

    Strange Resonating Ringing Singing Sound Carrier 40MPHA 38MPRA Mini Split Indoor Unit

    Is the inverter causing ringing through the compressor, and it's resonating through the unit? I have seen what sounds like the ringing/whining of bad bearings come through inverter driven motors. I'm not familiar with Carrier mini splits, but I assume there is a test mode where you can ramp the...
  11. G

    Regulator Pressure Adjustment Not Working

    I assume you are on natural gas. One issue I immediately see is your line/inlet pressure drops below the manufacturer recommended minimum of 5" WC under load. That tells me your gas line is likely undersized or has too much demand on it. That may be affecting the gas valves ability to make...
  12. G

    Big Maxx heat exchanger glowing

    That vent cap should be ok. You could try taking it off to see if it makes any difference. I would measure the flue temp to see how hot it is. If the flue temp is well above 450F, there could be an issue. 80K BTU may also be oversized for your application. Combustion analysis would be the...
  13. G

    Big Maxx heat exchanger glowing

    Manifold pressure is after the gas valve, on the burner side. Do you have the proper vent cap? Some caps if they are set too low can block the flue. Combustion analysis would determine if it's normal or not.
  14. G

    Big Maxx heat exchanger glowing

    Is there good flow from the venting? What does the manufacturer state for manifold pressure?
  15. G

    Unit heater gas valve sticking, freed by tapping, replace now or later?

    I would keep a spare on hand. Once the old valve finally gives up the ghost or becomes too annoying to deal with, then there is no major down time on the coldest days.