  1. L

    Which coating for new concrete floor

    That's what I was afraid of. I had read that pdf and saw the removal instructions outlined there. That might be above my skillset so perhaps I'll just learn to cope with the dust. Thanks for the input.
  2. L

    Which coating for new concrete floor

    So I'm almost done with the drywall in my new shop and I'm looking at the possibility of covering the bare concrete floor. The slab was poured in March and the contrator used a product called Rez-Seal from Euclid Chemical. The information I could find online says that this is an "acrylic polymer...
  3. L

    Question about breaker/fused disconnect sizing

    Yes, the breaker I'm referring to is the one in the panel feed. As far as a fused disconnect, that's all that was available locally, so it's what I'm using. I have included an outlet near the unit! That will probably come in really handy one day.
  4. L

    Question about breaker/fused disconnect sizing

    Thanks for the clarification. It was the "Minimum Circuit Ampacity" that threw me a bit as this is the first time I'd seen that.
  5. L

    Question about breaker/fused disconnect sizing

    Norcal - Thanks for the info but just so I understand, why is 14ga good with a 25A fuse or circuit breaker? I've always heard/read that 14ga/15A, 12ga/20A, etc. Is it because it's an HVAC system?
  6. L

    Question about breaker/fused disconnect sizing

    Ok, so 20 amp breaker and 25 amp fuses. That makes sense. Thanks for the help guys.
  7. L

    Question about breaker/fused disconnect sizing

    I'm working on a mini split install and ran into something that I'm not sure about. The unit is a Mr Cool DIY 2 ton mini split. I've used 10ga. wire to supply the unit and the only disconnect I could find seems to require 30A fuses. The label on the compressor reads as follows: Outdoor Fan...
  8. L

    I love my TLPPC floor.

    This is exactly what I'm looking for! Now to call Justin and ask a few questions.