  1. G

    air duct sizing, 30x40 detached shop

    I would say your calculations are more accurate than your friends. 8" for the smaller rooms should work well, just use take-offs that have dampers for any needed air adjustments. 14" for the large area looks good too.
  2. G

    Am I being oversold?

    18k for cooling is likely adequate, but the BTUs required for heat may be warranting 24k. The hyper heat type models are able to go down to -15F for heat, so make sure the other units you spec out can do the same.
  3. G

    Only 24k for 1800sqft?

    If the space is maintaining the setpoint without excessive run times under normal operating conditions, then you have sized the unit correctly. Sounds like your garage is pretty well insulated, thus allowing for a little bit smaller unit vs. going solely on square footage.
  4. G

    Mr Cool vs Blueridge 36k minisplit

    I've installed both Mr Cool and Blueridge furnace and central AC's. Both are nearly identical. No complaints of quality given the price. I also just became an authorized distributor in the state of Wisconsin for Mr Cool. I think you'll be good with either one.
  5. G

    Adding r410a to minisplit with unknown charge

    The manufacturer charging chart should get you close to where you need to be. ODT is for outdoor temperature, the slash numbers for IDT (indoor temperature) appear to be for wet and dry bulb temps. Is there a reason you can't pump down the lineset and evap into the condenser, or is that where...
  6. G

    Zoro Deals Thread

    Anyone have a 20 or 15 percent coupon they don't need? Zoro never seems to send me anything anymore...
  7. G

    Zoro Deals Thread

    Agreed, the service seems to be declining, unfortunately. I'm also thinking about taking my money elsewhere.
  8. G

    Supply house.com

    Great place to get HVAC and plumbing stuff. No complaints or issues with them. Shipping seems to be pretty quick as well.
  9. G

    Fix or replace inducer blower housing leak?

    It is still possible but I wouldn't suspect a bad heat exchanger on a 6 year old furnace. There might be a crack in the condensate collector/header box. This is the part that sits behind the inducer motor. If it's not an emergency, I would wait to disassemble anything until spring. Just make...
  10. G

    Fix or replace inducer blower housing leak?

    If you have a mystery leak with no obvious trace in sight, it is probably a good idea to check the secondary heat exchanger. Best way to do that is to remove the blower fan in the lower compartment and see if there is rust or water on the bottom of the secondary heat exchanger. If you see...
  11. G

    Big Maxx heater question

    You're likely going to need a manometer to troubleshoot any further. According to Mr Heater, gas line pressure on the INLET of the gas valve needs to be at least 13" WC. On the outlet of the gas valve, under fire, the burner/manifold pressure should be right around 10.4" WC. You may have too...
  12. G

    Mr Heater Big Maxx 50000 btu heating issue

    According to Mr Heater, with propane/LP, you need 13" WC to the INLET of the gas valve. After the gas valve (burner side/manifold) you should be at least 10.4" WC. Sounds like you may need a different regulator. Under fire the burner pressure should be at least 10.4" WC.
  13. G

    Exhaust vent Reznor Fe75

    I've never installed a heater like that, but I would assume that so long as your vertical piping is more than 75 percent of your horizontal, then it should be considered a vertical install.
  14. G

    Big Maxx heater question

    I agree that it should cause an error code under normal circumstances. I have seen odd instances where flame and pressure switch issues for some reason won't cause a fault indication. Hard to troubleshoot without seeing the unit run. Not sure if the board on the Big Maxx heaters use a timer to...
  15. G

    Exhaust vent Reznor Fe75

    Venting can be pretty confusing compared to older code. The way I'm reading current requirements, the system is defined as vertical if the horizontal distance is less than 75% of the vertical distance. So if it's vertical, you can use Cat 1 B vent. If it's horizontal, you need to use Cat 3...
  16. G

    Big Maxx heater question

    If the burner is turning on and off during a call for heat, you may have poor carry over on the burners due to incorrect gas pressure, dirty burners (sooted) or a flame sense issue. Easiest thing to do is clean the flame sensor with some emery cloth or a wire brush and see if that corrects the...
  17. G

    Thermostat issue, I think

    Unit is wired correctly. Like others have said, check thermostat programming to make sure it's not programmed for a different temperature. Thermostats are cheap enough, I would just replace it and eliminate that as the issue.
  18. G

    Thermostat issue, I think

    It appears you have wired it correctly, but without having a schematic of the heater it's hard to know for certain. If you have a multimeter, an easy test to determine if the stat is at fault is to put the leads at heaters terminal block across R and W. When the room reaches the temp setpoint...
  19. G

    Mr Heater Exhaust vent

    Tee should connect right in with your existing piping. The Selkirk B vent catalog shows exactly how to connect it with the lock tabs. B vent doesn't technically need to be air tight, but red high temp silicon on the cap won't hurt anything. Cap should press or be tapped in with a mallet without...
  20. G

    Mr Heater Exhaust vent

    Looking at your pics, it appears you should only need the flex pipe, tee and cap to make it work. The flex pipe has one end that already has the 'draft hood' connection, the other end should connect to your tee so long as the horizontal run is under 2.75 ft. Flex vent would be your horizontal...