Search results

  1. J

    SK Customer service

    I came across an SK 1/4'' ratchet i didn't know i had the other day. It was pretty siezed up, cleaned and lubed it and it won't ratchet. I read here somewhere about emailing there customer service. I emailed them Sunday night and got an email back Monday morning that a rebuild kit was on the...
  2. J

    Bosch Pitbull Extreme Rotary Hammer drill

    Hey all, I just wanted to comment on this drill i just purchased. I am running new electrical service to a pole barn i just put up and bought it to drive a couple ground rods. I was skeptical that it would be up to it, I couldn't find a lot of reviews of people using these smaller rotary...
  3. J

    New Polebarn Power feed

    I think 1.5'' should be fine too...how about the junction box size?
  4. J

    New Polebarn Power feed

    One last thing...Where the 2-2-2-4 MHF comes above ground what size conduit should i use 2''? and how about the size of the junction box, i'll have the 2'' (or ?) MHF conduit coming in the bottom and the 2-2-2-4 SER cable coming into the back, how should that enter ser clamp seeing it won't be...
  5. J

    New Polebarn Power feed

    Thanks everyone...I think i got it straight now. Just need a source for MHF by the foot.
  6. J

    New Polebarn Power feed

    Yea i thought of piping inside the house but the cable costs me about the same minus the extra labor of piping so i decided against it. So what is URD used for if it cant be brought inside..pole to pedestal only huh? JG
  7. J

    New Polebarn Power feed

    Ok..Gotcha. So i'll use MHF from the junction box on the outside of the house piped where above ground and to the panel in the barn. Thanks for clarifying that, didn't realize URD couldn't be used inside in conduit. Thanks JG
  8. J

    New Polebarn Power feed

    Yep..The URD will all be outside except for the run in conduit to the panel in the barn. Thanks
  9. J

    New Polebarn Power feed

    Hi All, I just put up a 24x32 polebarn and now am going to get some power to it. I was hoping some of the electricians in the group can check my plans. I have a 150A main panel in the basement of my house, i plan on running about 90' of 2-2-2-4 SER cable from a 90A breaker through the basement...