  1. T

    Running 100A service from house to new shop

    I haven't connected up the panel yet, I keep getting conflicting information as I'm browsing around the site looking at other things. The 2/0 wire is good to about 125A at the 175ft distance I'm running it, so isn't it dangerous to backfeed it with the 200A main? Sorry to keep dragging this...
  2. T

    Review of $15 Lights of America 8055SS 4' (2) T8 fixture

    Thanks for the warning, I just spotted these as well as the white ones at wally world over the weekend. How are they in cold weather? I think I saw on one of the boxes they would start at -20F.
  3. T

    Running 100A service from house to new shop

    Thanks for the info guys. I have decided to return the breaker and save the $70. I'll be hooking the 2/0 into the pass-thru lugs at the house (which is fed from the 200A main), and I'll have a 125A main in the panel out at the shop, roughly 175ft away. Should be fine right?
  4. T

    Running 100A service from house to new shop

    I could still kill the 200A main in the panel and it would kill the shop panel... only difference would be if I add a 125A breaker then I could kill the shop panel at the house and leave the others on.. which right now is just the single 30A for a RV receptacle. I already bought the 125A...
  5. T

    Running 100A service from house to new shop

    Thanks, I suspected as much.. I should just use #4 or #6 copper I have a 125A main breaker in the panel in the shop. Originally I had intended on adding a 125A breaker to the panel at the house to feed it because I only have 2/0 wire. But then I saw the pass-thru lugs and I just wanted...
  6. T

    Running 100A service from house to new shop

    Thanks, I wouldn't consider using the aluminum except that I have about 10ft of it left over. So there wont be any issues with the aluminum corroding due to soil or moisture? Another thing I realized is that the 200A panel that is going to be feeding the 125A panel in the shop has "feed-thru"...
  7. T

    Wire Marking Question

    This is the exact same boat I'm in.. same wire already ran in conduit except it's 2/0-2/0-2/0-1.... I ran it in conduit the whole way to my metal building... 2/0 MHF is what I really wanted, but its almost impossible to find. You can pick it up at the home improvement stores, but only in #2 or...
  8. T

    Running 100A service from house to new shop

    Got the conduit/wire ran this weekend.. This 2/0 wire is going to be a total pain to bend and fit into a breaker. Also, the 2/0 common and the #1 ground somehow I have to bond and get under the main lug in the main panel... do they make lugs that act as a splitter? Here's another question, can...
  9. T

    Running 100A service from house to new shop

    Finally got this ordered today, 2/0-2/0-2/0-1 ran me $2.14 a foot.. So just so I make sure I have this straight, I have a panel on the outside of my house that is connected to the meter loop. This panel has a 200A main, with spots for individual breakers below. The plan is to add a 100A -...
  10. T

    Running electric out to Pole Barn Basics

    I don't get it, all the supply houses around here only carry MHF in 2-2-2-4, or 4/0-4/0-4/0-2/0.. I'm running 100A service approx 150ft and the former is way too small and the latter is way to big.. It's almost impossible to find 2/0-2/0-2/0-1. I found 1 company that could order it, but they...
  11. T

    Running 100A service from house to new shop

    Well in my case the wire will enter the shop in the conduit before it enters the inside panel.. I suppose in this case MHF wouldn't be up to code in this 3' spot. I had found some 2/0-3 here locally for $1.57ft, and the 2/0-3 plus #1 is $2.41 a foot.. I guess I need to call back and find out...
  12. T

    Running 100A service from house to new shop

    So I actually need both a ground back to the main panel (EGC) and a ground rod at the garage , effectively connecting the 2 together? Same here, 2" conduit already through the slab.. I'm having some trouble tracking this down, most places have 2/0-3 but they don't have the 2/0-3 plus ground...
  13. T

    Running 100A service from house to new shop

    When I built my house, I had a 320A service put in so I could dedicate a 100A subpanel to running out to the shop when I built it. The panel is in place, and has a 100A main breaker. I plan on adding another panel at the shop with a 100A main, and individual breakers for the lights, outlets...
  14. T

    My Father's day gift: 30x50 shop build

    thanks guys, now I just have to get power and water back there this is the software I used to make the rendering, pretty cool stuff, free too: http://www.sweethome3d.com/index.jsp
  15. T

    My Father's day gift: 30x50 shop build

    Since I'm new to the forum, and building a shop, I felt this was the appropriate place to introduce myself.. Over Father's day weekend I was presented with a gift from my wife: A binder containing updated quotes for the shop that I had originally gotten in 2006 as well as the means to pay for...
  16. T

    Anyone used Zep floor sealers?

    It's a new floor that was poured about 4 weeks ago. I had intended to hit it lightly with the pressure washer, then apply the sealer. Thanks guys, I just didn't want to regret ever having laid eyes on this stuff :)
  17. T

    Heat pump for shop?

    I'm considering the same thing for my 30x50x13, although I was looking on craigslist for something around a 5 ton. The winters here in Arkansas aren't usually that bad, on the other hand the summers can be pretty miserable. In June of this year, we had temps pushing 110F.
  18. T

    Anyone used Zep floor sealers?

    - bump - Nobody?
  19. T

    Anyone used Zep floor sealers?

    I picked up a Gal of this stuff at a yard sale for $5 http://www.homedepot.com/buy/cleaning/professional-cleaning/zep/stain-resistant-floor-sealer-gallon-61906.html#specifications Has anyone here used it on anything? It says it covers approx 1500 sq ft., which is exactly the area of the slab...
Top Bottom