    Need help with some electrical work in shop...

    Yes sir, I might wind up doing just that.....Thank you for your help sir....
  2. S

    Need help with some electrical work in shop...

    Guys this is a mess that I came into just a few weeks ago.... This was a shed turned into a shop.... It is way out in the country and there seems to be some sort of deal or something worked out with the poco... None of my business....I don't and never will ask that question.... I just got...
  3. S

    Need help with some electrical work in shop...

    Guys I am grateful for every ones help....Please forgive me for not being able to navigate through this site.... I am trying to send pics....Don't know who's getting them.... I think a few people got them.... Just know I appreciate every ones help...
  4. S

    Need help with some electrical work in shop...

    Sir you are correct, there was a disconnect at the meter about 30 feet away, however there was no earth ground.... Does that still make it the main panel.... These pictures are the wires coming into the shop..... I guess this is not the main then.... The disconnect breaker is under the meter...
  5. S

    Need help with some electrical work in shop...

    Yes sir, I believe that you are right.... I
  6. S

    Need help with some electrical work in shop...

    I am so sorry Sir I am trying to navigate through this web site..... It would be easier to create a web site than what I'm experiencing ....
  7. S

    Need help with some electrical work in shop...

    Yes sir, let me try this once again... sorry...
  8. S

    Need help with some electrical work in shop...

    There is a disconnect at the meter, and yes sir, I was calling this the main panel.... The meter is about 30 feet away outside... And there is no earth ground there either....
  9. S

    Need help with some electrical work in shop...

    Sir, this is all I could get today.... I took the out going neutral to the sub and connected it to the grounding lug.... Because everyone told me that if I only had 240 volt circuits then I didn't need a neutral wire.... So now that wire is a ground....However, I still don't have an earth...
  10. S

    Need help with some electrical work in shop...

    Yes sir, I will try to get better pictures tomorrow....Sorry.....
  11. S

    Need help with some electrical work in shop...

    Hello Sir, I walked out there to the meter and finally got the box open and there was a 200 amp disconnect breaker right under the meter... This is the " Main Panel " coming in from the meter.... Notice there is no earth ground.... I took the neutral wire out of the lug that led to the...
  12. S

    Need help with some electrical work in shop...

    Yes sir.... I appreciate your help.....
  13. S

    Need help with some electrical work in shop...

    Thank you for your help sir....
  14. S

    Need help with some electrical work in shop...

    Sir, Thank you very much for taking the time on your weekend to fully explain how A.C. works.... Using the other hot wire as the return... The person who was teaching me is no longer around; however, I had asked him this question several times and I couldn't get any reasonable answer that would...
  15. S

    Need help with some electrical work in shop...

    I know this might be a dumb question, but if fault current goes back on the neutral, why do we even have a ground wire, and ground rods... Please if you would explain to where I can actually understand this....I would be grateful....
  16. S

    Need help with some electrical work in shop...

    There is no dis connect sir...The wires coming from the main are connected directly to the top of the sub lugs...