Need help with some electrical work in shop...

To avoid these ads, REGISTER NOW!
OP
S

Smarthomes.Cal

Well-known member
Joined
Oct 27, 2023
Messages
47
Location
Seattle Wa.
Sir you are correct, there was a disconnect at the meter about 30 feet away, however there was no earth ground....
Does that still make it the main panel....
These pictures are the wires coming into the shop.....
I guess this is not the main then....
The disconnect breaker is under the meter....
Does that make it the main panel instead of this one.....
 
OP
S

Smarthomes.Cal

Well-known member
Joined
Oct 27, 2023
Messages
47
Location
Seattle Wa.
Oh boy.....

Unless I'm missing something the black wire exiting upper right needs to be in conduit

Screenshot_20231030-174952.png
Oh boy.....

Unless I'm missing something the black wire exiting upper right needs to be in conduit

Screenshot_20231030-174952.png
Oh boy.....

Unless I'm missing something the black wire exiting upper right needs to be in conduit

Screenshot_20231030-174952.png
Need a little correction here. Fault current wants to go back to the neutral at the transformer. This is why the main panel is grounded. A ground rod, ect doesn't carry fault current.
Need a little correction here. Fault current wants to go back to the neutral at the transformer. This is why the main panel is grounded. A ground rod, ect doesn't carry fault current.
I'll throw in $1 and say it's all perfectly fine once pics are posted.
 
OP
S

Smarthomes.Cal

Well-known member
Joined
Oct 27, 2023
Messages
47
Location
Seattle Wa.
Guys I am grateful for every ones help....Please forgive me for not being able to navigate through this site....

I am trying to send pics....Don't know who's getting them....

I think a few people got them....

Just know I appreciate every ones help...
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,856
Location
NW Iowa
Oh boy. Subpanel wiring has lots of issues. It's tapped ahead of the main. That wire needs to be in conduit.

I assume the panel in the picture is what you have been calling the main panel? That looks pretty good. Other than the three loose wires
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,112
Location
Central Iowa
Oh boy. Subpanel wiring has lots of issues. It's tapped ahead of the main. That wire needs to be in conduit.

I assume the panel in the picture is what you have been calling the main panel? That looks pretty good. Other than the three loose wires
I've got a PM going on with him. There's a disconnect outside that he doesn't see any evidence of a ground at. The "main" panel has a three wire feed in what looks like PVC. I asked him to post more pics tomorrow, hopefully of the inside of the disconnect, maybe there's evidence of a UFER.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,112
Location
Central Iowa
Guys I am grateful for every ones help....Please forgive me for not being able to navigate through this site....

I am trying to send pics....Don't know who's getting them....

I think a few people got them....

Just know I appreciate every ones help...
your pictures are posting, I can't speak for everybody, but I am unable to blow them up big enough to tell anything.
 

Wiz02

Well-known member
Joined
Jul 13, 2007
Messages
2,399
Location
Southeastern PA
Guys I am grateful for every ones help....Please forgive me for not being able to navigate through this site....

I am trying to send pics....Don't know who's getting them....

I think a few people got them....

Just know I appreciate every ones help...
Like the others already said, your pics are uploaded and visible, but are very blurry.

While I may ask the guys here for a clarification on how the NEC is interpreted / implemented in the field under certain conditions, I understand how AC works and I am comfortable working with it. I strongly suggest given your level of experience, (based on your questions) that you hire a professional, licensed electrician.

I don't give this advice lightly, as I am a big proponent of DIY, and while people here are kind and want to help, you could end up getting seriously hurt or hurt someone else. Be safe.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,214
Location
NJ
OP, as requested better pics and include main panel on the pole, this "main panel" (let's call it Sub-1) and pics of Sub-2.
 
To avoid these ads, REGISTER NOW!

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,968
Location
Austin, TX
If you can pass an electrical inspection with the guys on GJ, you're dong it better than about 95% of the master electrician installs that I've seen in real life...
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,186
Location
Modesto, CA
Sir you are correct, there was a disconnect at the meter about 30 feet away, however there was no earth ground....
Does that still make it the main panel....
These pictures are the wires coming into the shop.....
I guess this is not the main then....
The disconnect breaker is under the meter....
Does that make it the main panel instead of this one.....
yes
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,112
Location
Central Iowa
In post #46 he states this is a brand new building. HIs location is Seattle. Does Seattle or the suburbs not have an inspection process? In a PM, he told me this is his job. I would be letting whoever owns the building, whether it's his boss or a land lord, know about this mess. Someone paid for that.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,186
Location
Modesto, CA
In post #46 he states this is a brand new building. HIs location is Seattle. Does Seattle or the suburbs not have an inspection process? In a PM, he told me this is his job. I would be letting whoever owns the building, whether it's his boss or a land lord, know about this mess. Someone paid for that.
oh theyre very strict up there from what ive heard...

theres no way this was inspected or permitted.

some of it needs to be ripped out and redone
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,112
Location
Central Iowa
oh theyre very strict up there from what ive heard...

theres no way this was inspected or permitted.

some of it needs to be ripped out and redone
I know all about sneaking things past building departments without a permit. One thing I haven't been able to figure out how to do is get a POCO to turn on the power to a building without a release from the AHJ.
 
OP
S

Smarthomes.Cal

Well-known member
Joined
Oct 27, 2023
Messages
47
Location
Seattle Wa.
Can you clarify this? The sub panel has no breaker/disconnect?
Can you clarify this? The sub panel has no breaker/disconnect?


oh theyre very strict up there from what ive heard...

theres no way this was inspected or permitted.

some of it needs to be ripped out and redone
Guys this is a mess that I came into just a few weeks ago....
This was a shed turned into a shop....
It is way out in the country and there seems to be some sort of deal or something worked out with the poco...

None of my business....I don't and never will ask that question....

I just got here, and I knew something was wrong.....

This is why I've reached out to you guys....

Yes the code in Seattle is very strict... Obviously this mess wouldn't pass....

We are so far out in the wilderness that a Black Bear is probably the code inspector....

Don't know .... never seen him.....
Probably won't.....

But what I've learned from you guys in just a few days has been extremely beneficial and for that I'm grateful....

Thank you guys for all of your help.....
 
OP
S

Smarthomes.Cal

Well-known member
Joined
Oct 27, 2023
Messages
47
Location
Seattle Wa.
Like the others already said, your pics are uploaded and visible, but are very blurry.

While I may ask the guys here for a clarification on how the NEC is interpreted / implemented in the field under certain conditions, I understand how AC works and I am comfortable working with it. I strongly suggest given your level of experience, (based on your questions) that you hire a professional, licensed electrician.

I don't give this advice lightly, as I am a big proponent of DIY, and while people here are kind and want to help, you could end up getting seriously hurt or hurt someone else. Be safe.
Yes sir, I might wind up doing just that.....Thank you for your help sir....
 