Given the information I would use 12. However I would temper the choice with knowledge of the load the motor sees and if it starts under load.

lg
no neat sig line
 
To avoid these ads, REGISTER NOW!
OP
M

mrbreezeet1

Banned
Joined
Dec 6, 2010
Messages
3,694
Location
Moundsville, WV, 15 miles South Of Wheeling WV
Well, a fellow at another group answered as below, so I had to get to Cardello's before 1:00 PM.
I went with 11 feet of the # 14/3.

mrbreezeet1 said:
. . . do I need to use # 12, or can I use # 14. Distance from outlet (20 amp) to motor will be about 10 feet.

Sounds like you're asking about cord, not building wiring. Typical thermoset and thermoplastic cords, like SO and SJO are rated 18A for 14 gauge (two current-carrying conductors, ground doesn't count) and 25A for 12 gauge.

Your call.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
Come on. #14 is rated for 15 amps. Running it at 14.7 amps doesn't make sense.

If it was hardwired & not useing Romex + the motor having overload protection, 14 AWG is allowed to be considered as 20A wire. Cord & plug connected will have to use the normal more restricted rules.
 