100 amp circuit II for phase converter.

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
23,094
Location
Amarillo,TX and Stinnett,TX
I started a thread a while back on using 2ga aluminum wire for this circuit. I ended up buying a spool of 1/0 copper wire. While in the shop today I had a few questions.

1. If I understand this correctly I can add a 100 amp breaker to the current panel and tap off of that. I want to start/run a 30hp three phase motor for a phase converter(FLA is 71.6 amps on 230v).

2. Can I run off the panel into a 100 amp disconnect (fused)? instead of a main lug or panel? I don't need extra circuits just the 100 amp one.

3. From the converter I would like to feed it into a three phase panel I already have.
 

Attachments

  • 042.jpg
    042.jpg
    118 KB · Views: 28
  • 039.jpg
    039.jpg
    78.8 KB · Views: 22
  • 087.jpg
    087.jpg
    92.6 KB · Views: 39
Last edited:
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
The 1/0 Cu is fine for 100A. A 100A fused disconnect box fed from a 100A breaker in the main breaker panel is fine. From that point on with the 3 phase you're on your own. :dunno:
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
You don't need a neutral for straight 240V. The neutral is only needed to get 120V. I don't know a thing about the 3 phase converter as to if it needs a neutral.
 
To avoid these ads, REGISTER NOW!

joe_padavano

Well-known member
Joined
Feb 26, 2011
Messages
1,788
Location
Northern VA
You don't need a neutral for straight 240V. The neutral is only needed to get 120V. I don't know a thing about the 3 phase converter as to if it needs a neutral.

If your three phase equipment has any 120V components, you'll need a neutral.

120-208-3-phase-surge-AG208C3-a.jpg
 
OP
9

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
23,094
Location
Amarillo,TX and Stinnett,TX
I have a 100 amp disconnect (three phase)that's rated for 15 hp max on single phase 240v & 30hp max on three phase. I want to use it to start a 30 hp three phase motor(idler) on 240v single phase. I know the hp numbers don't match and I have started the motor with this disconnect before.

I'm trying to not cause an electricial issue in my shop, my plan is to run a 100 amp circuit from the main panel with 1/0 copper wire to the disconnect. This will start the 30 hp idler. Do I need to move up to a 200 amp disconnect or is this wiring voodoo? Thank you!
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
You do not need a neutral w/ a phase converter, & the manufactured phase must not be used for any single phase loads.

NEC Art. 455 covers phase converters, here is a copy & paste of 455.6(B) 2011 edition.

(B) Manufactured Phase Marking. The manufactured
phase conductors shall be identified in all accessible locations
with a distinctive marking. The marking shall be consistent
throughout the system and premises
.

Italics added.

My personal opinion is to use orange for the manufactured phase just like the high leg of 240V 3Ø delta but it is not required to use orange....
 