To avoid these ads, REGISTER NOW!

12/3 and 20 amp breakers

mikhett

Well-known member
Joined
Sep 21, 2007
Messages
107
Location
jackson nj
Im getting ready to wire my 32x32 PB.My panel is a siemans I want to use 20 amp breakers and I have 250feet of 12/3 romex.They breakers say 14/3.Can I use the 12/3? thanks Mike
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Huh?

Not sure what youre referring to on the breakers. Breakers dont list NM-b wire gauges they only list a range of wire sizes that will fit in the breaker lug. Perhaps it says #14-3 awg??

Do u have a pic?
 

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,512
Location
East Bay SFO
I'm with wylie on that.
BTW, It would be wrong to install a 20 amp breaker on a circuit wired with 14 ga. wire.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
I'm with wylie on that.
BTW, It would be wrong to install a 20 amp breaker on a circuit wired with 14 ga. wire.

Not necessarily. For general purpose circuits yes, for motor and AC circuits no. On those circuits breakers are allowed to be lager than the wire ampacity

Maybe it only takes 14 gauge wire

In all my years in the field i have NEVER seen a breaker that only takes #14.
 
OP
M

mikhett

Well-known member
Joined
Sep 21, 2007
Messages
107
Location
jackson nj
Siemans 20 amp circuit breaker "ACCEPTS 14AWG WIRE".It accepts 14 awg wire .My question since I have 250 of 12/3 romex can I use it with these 20 amp breakers?
 

JRC3

Well-known member
Joined
Jun 30, 2014
Messages
12,481
Location
Southwestern OH
I would use nothing but 12.

Your 250', is that 3 wire with a red and a ground? If you're running it to 120v outlets I'd keep that for a more suitable purpose and go buy some 12-2.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Siemans 20 amp circuit breaker "ACCEPTS 14AWG WIRE".It accepts 14 awg wire .My question since I have 250 of 12/3 romex can I use it with these 20 amp breakers?

Ok. #12 should fit fine.

What is the circuit for?

Why do u need **/3- conductor?
 
OP
M

mikhett

Well-known member
Joined
Sep 21, 2007
Messages
107
Location
jackson nj
I got it cheap 250ft for 50.00 12/3. Im running it to all my outlets and switches using 20 amp breakers.
 

laser3kw

Well-known member
Joined
Nov 17, 2012
Messages
7,276
Location
northen IL
I Googled "Siemens 20 amp circuit breaker"
every image I found and zoomed in on shows printed on the breaker body, "AWG 14-10" usually followed by the torque spec for the lug.
"14-10" I would take to mean it will accept 14ga thru and including 10ga..
 
OP
M

mikhett

Well-known member
Joined
Sep 21, 2007
Messages
107
Location
jackson nj
YES,Wylie a 32x32 pole barn .The wire is 12/3 blk,wh,red and grnd.Can I use it and not connect the red?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
sure u can but then whats the point? Youre wasting the conductor and then only saving about $7 vs the cost of 12/2.

U should do a MWBC(multi-wire branch circuit) with 2 duplex outlets at each box then u can have outlets on separate circuits in each box. However, U will need a double pole GFCI breaker if you go this route.
 
To avoid these ads, REGISTER NOW!

empa1968

Member
Joined
Jul 16, 2015
Messages
18
Your breaker is your weakest link so it trips before anything burns up or shorts. #12 is for 20amp breaker #14 is for 15amp breaker.
 

TractorJeff

Well-known member
Joined
Dec 8, 2013
Messages
3,309
Location
Elkhorn, WI
If he has 12-3, can't he run half the outlets on B/W and the other half on R/W with 2 single pole breakers? That way he won't half to worry about something at the other end or other side of the building tripping him out?
 

slow

Well-known member
Joined
Feb 26, 2006
Messages
2,596
Location
near Orlando
depends on if the wire is protected or not. Here in central Florida almost all garages are drywalled, but up north, and other places, left bare studs is more common which could cause an issue with unprotected romex.
 