Well-known member
Im getting ready to wire my 32x32 PB.My panel is a siemans I want to use 20 amp breakers and I have 250feet of 12/3 romex.They breakers say 14/3.Can I use the 12/3? thanks Mike
I'm with wylie on that.
BTW, It would be wrong to install a 20 amp breaker on a circuit wired with 14 ga. wire.
Maybe it only takes 14 gauge wire
Siemans 20 amp circuit breaker "ACCEPTS 14AWG WIRE".It accepts 14 awg wire .My question since I have 250 of 12/3 romex can I use it with these 20 amp breakers?
I got it cheap 250ft for 50.00 12/3. Im running it to all my outlets and switches using 20 amp breakers.
That's a good idea,Wylie.I will make use of the red conductor and do a mbwc.
Will this be in a garage?......wow........
Huh?
If he has 12-3, can't he run half the outlets on B/W and the other half on R/W with 2 single pole breakers? That way he won't half to worry about something at the other end or other side of the building tripping him out?
Pipe?