120/240 appliances

To avoid these ads, REGISTER NOW!

canbug

Well-known member
Joined
May 6, 2008
Messages
337
Location
Just North of Cow Town
A/C unit, hot tub, if you are in the country your water well pump. Most loads that are over 20 amps are possibility using 240Volt. That would be your 4 wire.

Tim.
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,540
Location
Minneapolis
A/C unit, hot tub, if you are in the country your water well pump. Most loads that are over 20 amps are possibility using 240Volt. That would be your 4 wire.

Tim.

The hot tub may require 120/240vac, but an A/C and a well pump are going to be 240vac only.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,674
Location
SE MI
I have a walk in cooler most don't have but I cant think of another thing I own besides a dryer and range has 4 wire feed to it.

With all of the electronic controls now a days, the only thing that actually runs on 120V AC on those appliances is the LIGHT BULB !
 

Brian_WK

Well-known member
Joined
Jun 30, 2015
Messages
1,177
Location
NE South Dakota
I have a walk in cooler most don't have but I cant think of another thing I own besides a dryer and range has 4 wire feed to it.

Most walk-in coolers now have a 120v gfci circuit ran to the inside and a 240v circuit ran to the condensing unit.

Some commercial reach in freezers do as well, others have a transformer for the electronics. Same goes for alot of commercial equipment that requires large heat or cooling loads if you are lucky enough to have it in your home. I once saw a water heater that had a digital lcd screen on it im assuming that had a neutral but never tore into it.

My old dryer was the same way was a 3 wire cord no electronics just buttons and a timer never bothered to look at how they did the light bulb. New drier needed a 4 wire. Checked it out in the wiring diagram only the light bulb and the control board needed 120v (which was again reduced lower and to dc) I removed the light bulb (it was bright enough for me in my laundry room anyways)and put in a transformer to reduce from 240v to 120v.

Problem solved only needed a 3 prong plug then.

Brian
 
Last edited:

Brian_WK

Well-known member
Joined
Jun 30, 2015
Messages
1,177
Location
NE South Dakota
With all of the electronic controls now a days, the only thing that actually runs on 120V AC on those appliances is the LIGHT BULB !

My oven has a fan for the convection side that runs on 120v must have been a deal on them instead of the 240v when they were manufacturing them.

Brian
 
To avoid these ads, REGISTER NOW!

nh_yota

Well-known member
Joined
Mar 10, 2015
Messages
4,097
Location
Seacoast New Hampshire
Submersible well pumps run on 240 and they don't use a neutral but they still require 3 conductor (or 4 conductor with ground) cable from the control box out to the pump. The start capacitor is in the controller and not the pump, so the cable has 3 conductors for start/run/common.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,279
Location
Modesto, CA
A/C unit, hot tub, if you are in the country your water well pump. Most loads that are over 20 amps are possibility using 240Volt. That would be your 4 wire.

Tim.

Only the hot tub will need a neutral.

With all of the electronic controls now a days, the only thing that actually runs on 120V AC on those appliances is the LIGHT BULB !

Have u ever taken apart a dryer? The motor in many of them is 120v.

My dryer is less than 10yrs old and has that setup.

Submersible well pumps run on 240 and they don't use a neutral but they still require 3 conductor (or 4 conductor with ground) cable from the control box out to the pump. The start capacitor is in the controller and not the pump, so the cable has 3 conductors for start/run/common.

Beat me to it!
 
OP
S

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Yes from the control box for a well but that's a different animal than a common feed, The one I forgot about was the hot tub, I knew there was something else but couldn't remember. No garage tools though? I got a lot of stuff but cant think of a single place a guy would benefit from capping an extra wire.
 
Last edited:

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,796
In my own shop the only machine that could use a neutral is a 1976 Rockwell 20" wood/ metal bandsaw, because a extra blade welder is 120 volts. In my opinion, this is a rare situation, because a control transformer takes care of 120 volt power for the starter & light, existing welder is 240V it just does not work...

Other then hot tubs, clothes dryers, ranges/ cooking equipment it's wasting money to run a unneeded neutral.
 

Alchymist

Well-known member
Joined
Mar 1, 2009
Messages
4,423
Location
Central PA
My wood shaper has either 120 or 240 motor option, and I run it on 240. Unfortunately the power feeder is 120 volts. Only options are to convert back to 120 on the main motor, add a step down transformer for the feeder, or run feeder from a separate 120 outlet.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,279
Location
Modesto, CA
My wood shaper has either 120 or 240 motor option, and I run it on 240. Unfortunately the power feeder is 120 volts. Only options are to convert back to 120 on the main motor, add a step down transformer for the feeder, or run feeder from a separate 120 outlet.

Whats the FLC?
 

Alchymist

Well-known member
Joined
Mar 1, 2009
Messages
4,423
Location
Central PA
Whats the FLC?

Spec sheet says 12.5 @120V for shaper, and 1.2 for feeder. Would be almost 14 on 120 volts, doable on a 20 amp circuit I guess. However, a transformer for the feeder would bring the 240 Volt draw to just under 7 amps. Have some transformers salted away, just never got around to doing anything about it. :headscrat
 