scotty95
Active member
First off, happy holiday's to all. I have a new 230v air compressor that I need to wire up. Here is what I got. 2- 120v hots and 1 grd out of main panel in the house with single 40amp breakers. New 120/240 sub-panel in garage. I have a new 120/240v double pole breaker in garage for the compressor. I am only getting 120v thru my wires. So I checked both hots with each probe and I get nothing. Went down to the main panel, they each have 120v flowing, but when I touch both breakers for the 240v reading, I get nothing. Do I need to put a double pole breaker in the main panel, or try new 40a singles? I still need 120v in garage too. I am not an electrician, but have learned a ton on here and google. Thanks for any input, scotty.