120V-only Subpanel

Mattlt

Well-known member
Joined
Nov 30, 2005
Messages
1,382
Location
MN
Another thread mentioned a 120V-only subpanel. I thought if you ran a subpanel you needed to run 240V to it? Is a different kind of panel required, or is it all in the wiring?

I'm thinking of building a small shed and I'd like to have a couple of 120V circuits in it... 240 would be overkill in this situation.

I know 240 would be the ideal solution, but can someone school me on the 120V subpanels?
 
To avoid these ads, REGISTER NOW!

acer66

Well-known member
Joined
Dec 4, 2010
Messages
4,418
Location
Western North Carolina
If you have only one phase coming in it you would have a 120V panel,
meaning both bus bars at the Sub panel are on the same phase.
You could make any 120/240V panel I ever saw a 120V only panel
via wiring but I do not know how legal that is.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
If you have only one phase coming in it you would have a 120V panel,
meaning both bus bars at the Sub panel are on the same phase.
You could make any 120/240V panel I ever saw a 120V only panel
via wiring but I do not know how legal that is.

The nomenclature "phase" is incorrect when one is refering to a single phase(1Ø) source, "leg" is a more correct choice since 3Ø power is rare in residentail in the US & 2Ø power is a obsolete power system.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
how much power are you running to your shed? do you just want one (or two) circuits for lights and general use receptacles? if so you dont need a subpanel, just run 12/3 UF (or 10/3 or possibly larger depending on distance involved), or conduit in wire, and supply it with a 2P 20a breaker and youre complying with the one circuit rule that lets you not have a subpanel. not sure if a disconnect is required, i dont think so but if it is you can use a 20a 2P snap switch (toggle switch ie light switch)
 
OP
M

Mattlt

Well-known member
Joined
Nov 30, 2005
Messages
1,382
Location
MN
how much power are you running to your shed? do you just want one (or two) circuits for lights and general use receptacles? if so you dont need a subpanel, just run 12/3 UF (or 10/3 or possibly larger depending on distance involved), or conduit in wire, and supply it with a 2P 20a breaker and youre complying with the one circuit rule that lets you not have a subpanel. not sure if a disconnect is required, i dont think so but if it is you can use a 20a 2P snap switch (toggle switch ie light switch)

That's a good idea. That sounds about like what I want to do.
 
To avoid these ads, REGISTER NOW!

Berserker

Banned
Joined
Oct 17, 2010
Messages
222
Location
WI
You can put for circuits in subpanel without a disconnect. You could just run 10-2 and put in a couple 15 amp breakers. For a shed, you may just run 10-2 for distance, and one breaker.

I am not sure what the code is, I haven't done it. But if you only run one hot out there and have a subpanel set up for 220, you could do a jumper between the incoming lugs.

Size up on wire for every 100 feet, for voltage drop is a good rule of thumb.
 

Buzzy

Member
Joined
Mar 31, 2011
Messages
5
Wouldn't you need to run a Ground fault circit breaker as well?? I would think so because you are running a wire outside.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
Wouldn't you need to run a Ground fault circit breaker as well?? I would think so because you are running a wire outside.


no. 15 and 20 amp 120v receptacles must be gfci protected when outside or in a garage, but that doesnt mean you have to have a gfci breaker. You can use gfci receptacles, (or have one gfci receptacle supplying other standard receptacles from its load terminals)
 