How thick is the slab under the post? And is it reinforced? Any pre-pour pictures?Shop was built in January, builder was told lift placement. Should I be worried?
If you choose to dig out the area, dig deep. When I had my pad poured I described to the contractor what I wanted and why. His response was if I needed support in those areas, it was easy to take a couple of scoops extra or dirt out and make it thick in those ares. Heck go 18" or 24", it's just a little more work.cut out a block of concrete, dig down 12" or so, set re-rod into the existing slab and pour new concrete.
Well original plan was dead center where the cross is. The building ia 30x30 the builder added a I beam right above centerline for a trolly/hoist lift would have clearance issues there so it was moved back was told concrete is thick enough thru out slab. Most holes were right at 4 inches deep. Lift instructions said minimum of 4 inchesHow thick is the slab under the post? And is it reinforced? Any pre-pour pictures?
Don't believe there is a gap maybe due to angle on picture. I will go out n ck n see if I can get feeler gauge under it. If u look at picture close to wall u can see a shim I had to Install to get Column plumb. 3/4 anchors where included with my lift instructions state torque to 130 ft lbs which I did few weeks ago after seeing someone drop a truck.The root cause I think is that there is a gap between the plate and the concrete, which gives the concrete someplace to go. That whole joint is under tension all the time. A 3/4" bolt torqued up to 80 ft-lbs ~ 5000lbs of tension.
If it holds torque then I think you're OK, but I would shim out the gap.
Good eye there definitely is a gap. Not sure if it was always like that or due to shifting. Probably was like that but didn't give it alot of thought since it was square.The root cause I think is that there is a gap between the plate and the concrete, which gives the concrete someplace to go. That whole joint is under tension all the time. A 3/4" bolt torqued up to 80 ft-lbs ~ 5000lbs of tension.
If it holds torque then I think you're OK, but I would shim out the gap.
The bolt is loose has little wiggle to it. Think it would be fine with one bolt loose I've seen lifts with one bolt per column missing for years. Guess I will try n tighten it up seems like it may pull concrete up moreis it an optical illusion or is that bolt not perpendicular to the slab?
..... My point is that you get a lot of advice on here and need to filter it like any forum. Do yourself a favor and call the manufacturer.....
The AB in question is in bad spot due to bracket holding fixture. The AB is loose and can wiggle. I honestly think it's broke more than 1 inch on top. As far as drilling I did it all myself none were elongated but maybe drilled at slight angle. Instructions did say to try n drill all the way thru slab so AB can be knocked so the way thru if neededThis is not true
The stress is torsional on the pad under the post, not down pressure
unless there is new science. The weight of the lift and elevated vehicle must be supported by a vertical reaction, regardless of the other forces.
I think the torsion that everyone is referring to would better be described as a bending moment, the result of non concentric forces on the column. Torsion would be twisting of the column; rotation about its long axis.
It is better to grout the base plate so that the column vertical and bending loads are spread out over the area of the base plate. If you don't grout, the baseplate only contacts the floor at the high points of the concrete. This can cause problems or failures which would take too long to explain. Without baseplate grouting and leveling one column could be higher than the other which could cause additional problems at the baseplate concrete connection.
If you install a pad footing I strongly recommend you do not follow this suggestion: No rebar, no wire, no 24" hole etc etc. Just cut the hole and pour it again.
Concrete has little strength in tension and bending moments in the slab footing result in tension in the concrete. The reinforcing will hold the concrete together when it cracks, as it does most of the time.
If the pad footing cracks through the 12" thickness you will lose the benefit of the portion that is not connected to the column. There is more to this but it would take way to much time to go into.
Steel reinforcing is cheap, put it in, put lots of it in. If this were my own garage and lift I would place some #3 ties around the bolt group. You can get some bolt group reinforcing ideas from Hilti and maybe Simpson. Horizontal bars through the bolt group will also increase the strength of the connection.
This is cause for concern Well I went to ck torque on them all were fairly close except the one it was loose and wouldn't tighten didn't try to much just couple degrees n concrete started lifting more.r. I would not use this lift as it appears, from your description, that the AB is slipping in the hole and thus not connected to the concrete.
If I read this correctly Most holes were right at 4 inches deep. Lift instructions said minimum of 4 inches ; you used post installed anchors. If your slab is 4" thick and you drilled competely through the slab you may have other problems. All post installed AB's, that are approved by the code, must have ESR testing reports on the installation methods. Punching through the slab for the AB, or even getting close to the bottom of the slab (or footing) with drilled holes, would be contrary to the ESR reports and not approved by building code. Sometimes the drill punches out the concrete on the back side of the slab to form a reverse cone. If this happens you do not have the required concrete thickness.
AB holes drilled completely through the concrete can allow moisture or even ground water to enter the hole and corrode the AB.
Yea, I know that the lift mfg's recommend that you use methods that would not be approved by your local building codes. My view is that they have not kept up with current codes and are at risk for making these recommendations.
If AB's have 4" required emb and you lose the top 1" of concrete, see your photo, you only have 3" of emb. not the 4" required. Lose an inch at the top, see photo, and inch at the bottom due to blow out, and you have 2" less concrete at the AB.
It appears that the AB in question is installed at an angle. If the contractor mislocated the hole, or the bit drifted, and he then enlarged the hole to get the AB to align with the base plate hole, the AB wedge might not set in the oversized hole. This is if you used a wedge anchor. Most codes require that post installed anchors get special inspection for these, and other, reasons.
This is your opportunity to take a good look at your installation and make revisions
Kind of lost on bolt group mounting and grouting lift any more information on this? I'm a mechanic and been working in shops 20 years now haven't seen a lift grouted to concrete it makes since thoThis is not true
The stress is torsional on the pad under the post, not down pressure
unless there is new science. The weight of the lift and elevated vehicle must be supported by a vertical reaction, regardless of the other forces.
I think the torsion that everyone is referring to would better be described as a bending moment, the result of non concentric forces on the column. Torsion would be twisting of the column; rotation about its long axis.
It is better to grout the base plate so that the column vertical and bending loads are spread out over the area of the base plate. If you don't grout, the baseplate only contacts the floor at the high points of the concrete. This can cause problems or failures which would take too long to explain. Without baseplate grouting and leveling one column could be higher than the other which could cause additional problems at the baseplate concrete connection.
If you install a pad footing I strongly recommend you do not follow this suggestion: No rebar, no wire, no 24" hole etc etc. Just cut the hole and pour it again.
Concrete has little strength in tension and bending moments in the slab footing result in tension in the concrete. The reinforcing will hold the concrete together when it cracks, as it does most of the time.
If the pad footing cracks through the 12" thickness you will lose the benefit of the portion that is not connected to the column. There is more to this but it would take way to much time to go into.
Steel reinforcing is cheap, put it in, put lots of it in. If this were my own garage and lift I would place some #3 ties around the bolt group. You can get some bolt group reinforcing ideas from Hilti and maybe Simpson. Horizontal bars through the bolt group will also increase the strength of the connection.
This is cause for concern Well I went to ck torque on them all were fairly close except the one it was loose and wouldn't tighten didn't try to much just couple degrees n concrete started lifting more.r. I would not use this lift as it appears, from your description, that the AB is slipping in the hole and thus not connected to the concrete.
If I read this correctly Most holes were right at 4 inches deep. Lift instructions said minimum of 4 inches ; you used post installed anchors. If your slab is 4" thick and you drilled competely through the slab you may have other problems. All post installed AB's, that are approved by the code, must have ESR testing reports on the installation methods. Punching through the slab for the AB, or even getting close to the bottom of the slab (or footing) with drilled holes, would be contrary to the ESR reports and not approved by building code. Sometimes the drill punches out the concrete on the back side of the slab to form a reverse cone. If this happens you do not have the required concrete thickness.
AB holes drilled completely through the concrete can allow moisture or even ground water to enter the hole and corrode the AB.
Yea, I know that the lift mfg's recommend that you use methods that would not be approved by your local building codes. My view is that they have not kept up with current codes and are at risk for making these recommendations.
If AB's have 4" required emb and you lose the top 1" of concrete, see your photo, you only have 3" of emb. not the 4" required. Lose an inch at the top, see photo, and inch at the bottom due to blow out, and you have 2" less concrete at the AB.
It appears that the AB in question is installed at an angle. If the contractor mislocated the hole, or the bit drifted, and he then enlarged the hole to get the AB to align with the base plate hole, the AB wedge might not set in the oversized hole. This is if you used a wedge anchor. Most codes require that post installed anchors get special inspection for these, and other, reasons.
This is your opportunity to take a good look at your installation and make revisions
exactly why I wouldn't want anything less than 8" to start with. I was picturing that scenario when they talk about 4' long anchor bolts going into 4" thick concrete. If it's a new pour and you are planning a lift (and you should), take my contracts advice and go 12" thick (it's just a couple of scoops more when they are doing it).If I read this correctly Most holes were right at 4 inches deep. Lift instructions said minimum of 4 inches ; you used post installed anchors. If your slab is 4" thick and you drilled competely through the slab you may have other problems. All post installed AB's, that are approved by the code, must have ESR testing reports on the installation methods. Punching through the slab for the AB, or even getting close to the bottom of the slab (or footing) with drilled holes, would be contrary to the ESR reports and not approved by building code. Sometimes the drill punches out the concrete on the back side of the slab to form a reverse cone. If this happens you do not have the required concrete thickness.
Any pics of how u did 2 layers of steel?I found Mohawk's retro slab guide helpful. There's no recommendation in there even close to 4'x4', and they are specific on rebar requirements. Given the cost differential, error on the side of safety.
My retro slab pour ended up as a 4'x12' at about 14" thick with two layers of reinforcing steel.
Reference pdf document from Mohawk:
http://www.mohawklifts.com/consumer/library/Slab_Req-Reco_2-2010.pdf
![]()
I didn't really try n crank down on the AB with fear of doing more damage. The pic may not show but when I tried to pull out the piece of busted concrete it felt deepFrom above
My point is that you get a lot of advice on here and need to filter it like any forum. Do yourself a favor and call the manufacturer....
This is good advice with the following two caveats:
1. There is nothing in the mfg's instructions that suggest you should not make the installation stronger.
2.All lift mfg's will state in their installation instructions that you must comply with local codes.
Bendpak says it this way: I understand that the lifts are supplied with concrete
fasteners meeting the criteria of the American National
Standard “Automotive Lifts - Safety Requirements for
Construction, Testing, and Validation” ANSI/ALI ALCTV-
2011, and that I will be responsible for all charges related
to any special regional structural and/or seismic
anchoring requirements specified by any other agencies
and/or codes such as the Uniform Building Code (UBC)
and/or International Building Code (IBC).
Installation must comply with your local code.
Simpson strong tie wedge anchors, and all the other anchor mfgs of wedge anchors (post installed chemical anchors too)with ESR reports will be similar that the anchor bolt hole depth is less than the slab thickness. See ESR 1771http://http://www.icc-es.org/Reports/pdf_files/ESR-1771.pdf
See table 1 page 4 of the ESR report; other tables include some of the same information. Holes for wedge anchors may not punch through the slab. For 3/4" wedge anchors the minimum concrete thickness is 6-3/4"
The OP did not comply with Bendpaks requirements (the building code) for three reasons; his slab is not thick enough for 3/4" wedge anchors, he has an improper hole depth, and he did not get special inspection (see ESR 1771 page 3 section 4.4).
A possible reason the nut can't be tightened is that the wedge is below the bottom of the concrete. In any case there is a torque requirement for setting the wedges. If the bolt spins before the specified torque is acheived the AB installation has failed. The OP's wedge anchor, the one that is not tightened, does not comply with code, or Bendpak's requirements.
That the OP may have used another AB would probably not be sufficient to comply with code. All wedge anchor mfgs, that have produced ESR reports have similar criteria to the Simpson ESR report.
The wedge anchors bought from the bin at the hardware store; if they don't have an ESR report, they are not code compliant.
Though the OP claims that he complied with Bendpak's requirements by drilling through the concrete he violated their requirement to comply with codes. If the lift fails and falls he will be the responsible party. Don't even think that Benpak would let you win that argument in court.
OP, my intentions are not to pick on you but to motivate you to review your installation, and live long enough to get full use of your lift.
Re this question:Kind of lost on bolt group mounting and grouting lift any more information on this? I'm a mechanic and been working in shops 20 years now haven't seen a lift grouted to concrete it makes since tho Bendpak and all other lift mfgs require that the columns be plumb. With an uneven concrete surface this can not be accomplished without grout. (Use SIKA HSNS grout). I did not read the entire bendpak instructions but I would bet there are other requirements that suggest, if not categorically state, that the base plates be grouted. One way they could say this is they require the baseplate to bear evenly on the supporting surface.
There is a lot more to this than what I have said about anchor bolts and installation. I don't have the time to write it all out and explain it and no one would read it anyway. I don't want to argue, take it all as you wish. My sole intent is to educate a few people, that ones that are going to install a new lift, to give their installation serious thought. Be safe out there.
To be honest all I know is the contractor was informed I would be installing a lift, he had to follow criteria from city inspector. I've had lifts installed in buildings I've rented I've also worked in older and newer shops with lifts and never had this issue.Is that a post pensioned slab? If so, you should have your engineer of record look at things.
If not, do you have a plan that shows the reinforcing/slab plan for the floor?