220/110
48fordnut
mid ga
I need to get 110 off of a 220 outlet .how, with details. its a wall box going to my compressor. i need to pull the 110 off for a chop saw in another section of the shop. this is the closest.details please. thanks, jim.
Charles (in GA)
50 mi south of Atlanta
Problem is, the 220/240 outlet you have now probably does NOT have a neutral in it, most 220/240 doesn't. Without a neutral, you cannot get the 110/120 you want. You really need to run a new circuit. Save yourself headaches, illegal wiring, and all the rest. If you had a fire, insurance might deny due to the illegal/not to code wiring.
Charles
jerryW
Phx AZ
Oler code usually allowed the 220v circuit neutrall to go thru the ground. Newer code has a seperate neutral and ground. At least on appliances.
It would be safer to run a seperate cicuit for the chop saw.
jerry
bhays
Southern Indiana
MXtras said:
Maybe this will help explain things a bit.
Scott
That's a really nice diagram. Did it come from a particular web site, I would like to see more of those for different situations.
DIGGER_DAVE
Calgary AB Canada
Scott
Scott, your diagram shows the current NATIONAL method of Neutral/Ground ties at the INCOMING PANEL.
However before any one tries to use a ground wire in a 220 outlet as the NEUTRAL to create 110/120 volts; DON'T!
Almost ALL electrical codes in North America DO NOT allow the use of the ground for the neutral or visa versa. (in the event of a fire; your insurance could be "null and void" if you do it!)
The ONLY acceptable method of wiring a 110/120 volt outlet; is to start at the panel with a Single Leg breaker and run #14/3 gauge wire (minimum) to the needed outlet.
There IS one exception. IF! a NEUTRAL IS run with the two "HOTS" (220 volt) AND a GROUND - FROM THE PANEL (total of 4 conductors; wire #gauge to match breaker rating) a 110/120 volt COULD be "tapped off." (but it would now be rated at the amperage of the breaker)
This set-up is normally only used with combination 220/110 volt equipment (using a 4 prong plug - twist lok for example) where the 110 volt leg is protected by it's OWN breaker at the machine. The dual voltage arrangement is often found in industrial welding machines
rburke65
Canfield, Ohio
Boy, I'll say it's been a long time! Did you just run it now.....recently or did you run it back in '06 and you're just getting around to posting? Good to have you back.
daviomaron
The only safe way to do it is to make one of the hots into a neutral and downsize the breaker.
afe5232
PWC Repair
Arkansas
My whole house is wired like the little diagram. All my neutrals and grounds tie on to the same bar. That's just the way the older stuff was.