Guys How Many amps does a 80 Gal 220 V 5 to 7.5 HP Air compressor usally use?
ez-duzit said:My 7.5 hp compressor motor says 30 amps @ 220 volts.
I am wiring everything up, And I don't have the Compressor narrowed down yet. SO I want to get a rough Idea,
This is what I have,
I have a 220 run with 12 2 or 12 3 Romex with a double 20 Amp Breaker
then I have a much larger 220 with a 50 Amp Breaker.
I am not a electrical guy someone ran this for me, one was sup to be for a compressor and one for a welder.
I am wiring everything up, And I don't have the Compressor narrowed down yet. SO I want to get a rough Idea,
This is what I have,
I have a 220 run with 12 2 or 12 3 Romex with a double 20 Amp Breaker
then I have a much larger 220 with a 50 Amp Breaker.
I am not a electrical guy someone ran this for me, one was sup to be for a compressor and one for a welder.
Would the 50 Amp one work for the 7.5? The wire to that one is much larger.
WOuld the 12 3 work for a 5 Hp?
JOE.G said:Would the 50 Amp one work for the 7.5? The wire to that one is much larger.
WOuld the 12 3 work for a 5 Hp?
Yes, the 50 amp circuit would work for the 7.5 hp.
You'd probably need a 40 amp for the 5 hp, but that 12 ga cable is too small.
Posted from Garagejournal.com App for Android
I am looking at these two,
http://www.sears.com/shc/s/p_10153_12605_00916477000P
http://www.tractorsupply.com/en/store/ingersoll-randreg;-5hp-air-compressor-80-gal
I am unsure on the wire size on the 50 amp circuit but i can find out.
Perhaps I missed it but wire size depends on the distance run as well as the amps.
Distance does come into play but usually at distances greater than 100'. So for typical circuits within a house distance is not a wire size adjustment issue.
Sorry, but I beg to differ.
![]()
Nice try but thats for 12v DC wiring which is a whole different animal than AC wiring!
Nice try but thats for 12v DC wiring which is a whole different animal than AC wiring!

Sorry, but I beg to differ.
If the wire was sized based on a welder using the circuit, the wire might be too small as circuits feeding welders are allowed to be reduced in size!!
Good call -- for an extreme case (like a large motor or a long wire run).
But for the OP (who hasn't bought a compressor yet), I think chances are pretty good that the 50A circuit will be perfect for a 7.5 hp compressor. He'll definitely need to check his wire size to be sure it wasn't sized for a welder, but unless it's an extreme case, that 50A circuit should be adequate for a 7.5 hp motor (or less).
I say this because Joe's friend probably ran 6 AWG cable for that 50 amp circuit, if not, then it's gotta be 8 AWG (because it's "much larger" than the #12 Romex). A big box compressor will probably use a motor with FLA of about 32A -- post #9 here: http://www.garagejournal.com/forum/showthread.php?t=131410 -- which means 125 percent of the FLA is going to be right at 40A, so that would need 8 AWG cable. If he hardwires the comp to a disconnect, then I believe the NEC allows a 50A breaker on that circuit.
Please let me know if I have any of that wrong, because I'm hoping I can hardwire my 5 hp comp with 10 AWG cable and a 40A breaker.
Thanks,
Rick
pattenp said:If using romex, #10 NM-b is 30A max and #8 NM-b is 40A max. Being hardwired has noting to do with the breaker size. If you use THHN in conduit then #10 THHN is 35A and #8 THHN is 50A. The difference is romex is to be sized at 60 deg.C and THHN is sized at 75 deg.C.
Okay, now I'm confused -- I thought the NEC allows the breaker to be oversized (compared to a smaller wire size) for a hardwired motor, to allow for startup current draw???
So for a normal circuit, I would use a 30A breaker to protect 10 AWG cable. But for a hardwired motor, I can use a 40A breaker instead. Does that sound right?
Thanks,
Rick
Posted from Garagejournal.com App for Android
I think it is #6 Wire on the 50 Amp Circuit. I forgot to check today. I know he did not under size the wire.
So you guys are saying I should take the 50 Amp breaker out and put either a 30 or 40 amp breaker?
Also when you get a new compressor does it come with a wire to hook to the wall?
Can I put a plug on the end or does it need to be hard wired?
How many amps can 12 3 Romex take?

Good timing...My compressor is not a 7.5hp, For the time being I only have a 3hp...BUT I am about to start wiring it in the next few days. I WAS Gonna use 40A on #8 Romex...BUT now I'm second guessing myself in terms of future proofing.
If NEC Says a 7.5HP is 40A, is the 125% uprating for the purposes of Continuous duty? ie 3hours or more @ 100% utilization?