There is a difference between startup amps & running amps. Also depends on the PSI... The higher the pressure, the harder the pump & motor have to work, the more amps it will draw. You can literally clamp a meter on and watch as the pressure builds up your amps will increase.
 

Gary S

Well-known member
Joined
Dec 27, 2008
Messages
2,972
Location
Bismarck, ND
"Usually uses" isn't nearly as valuable to you as the Amperage numbers stamped on the motor nameplate. Start there and get the manufacturer's ratings.
 

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,872
Location
oregon
here is a chart you can go by

CHART

on edit

As a "rules of thumb" amps horsepower rating can be estimated as

115 Volts motor - single-phase : 14 amps/hp
230 Volts motor - single-phase : 7 amps/hp
230 Volts motor - 3-phase : 2.5 amps/hp
460 Volts motor - 3-phase : 1.25 amps/hp

lg
no neat sig line
 
Last edited:

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
By the NEC for sizing circuits you use the HP on the motor data plate, 5HP is 28A @ 230V and 7.5HP is 40A @ 230V.
 
OP
J

JOE.G

Well-known member
Joined
Feb 4, 2013
Messages
765
Location
Eastern ( Catskills ) NY
I am wiring everything up, And I don't have the Compressor narrowed down yet. SO I want to get a rough Idea,
This is what I have,
I have a 220 run with 12 2 or 12 3 Romex with a double 20 Amp Breaker
then I have a much larger 220 with a 50 Amp Breaker.
I am not a electrical guy someone ran this for me, one was sup to be for a compressor and one for a welder.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
I am wiring everything up, And I don't have the Compressor narrowed down yet. SO I want to get a rough Idea,
This is what I have,
I have a 220 run with 12 2 or 12 3 Romex with a double 20 Amp Breaker
then I have a much larger 220 with a 50 Amp Breaker.
I am not a electrical guy someone ran this for me, one was sup to be for a compressor and one for a welder.

The wire for motor circuits is sized at 125% of FLA of the motor, so #12 Romex would be too small for those motors!!

EDIT: Individual #10 THHN conductors would work for the 5hp and #8 THHN for the 7.5hp!
 
Last edited:

ez-duzit

Well-known member
Joined
Jun 24, 2013
Messages
5,094
Location
Marina del Rey
I am wiring everything up, And I don't have the Compressor narrowed down yet. SO I want to get a rough Idea,
This is what I have,
I have a 220 run with 12 2 or 12 3 Romex with a double 20 Amp Breaker
then I have a much larger 220 with a 50 Amp Breaker.
I am not a electrical guy someone ran this for me, one was sup to be for a compressor and one for a welder.

WAY too small for 7.5 hp.
 

ArmyVW_GuyInTX

ALLIANCE MEMBER
Joined
May 17, 2013
Messages
458
Location
North of the Fort Worth/Dallas metro area
I have an IR 7.5 HP/80 gallon that pulls 28amps on start-up according to the owner's manual.

I ran #6 awg to a sub panel and drilled through the wall to the compressor (outside on cork/rubber blocks but in an enclosure) and have a 30amp breaker for it years ago.
 
Last edited:

RickP

Well-known member
Joined
Jan 15, 2013
Messages
1,548
Location
Annapolis, MD
JOE.G said:
Would the 50 Amp one work for the 7.5? The wire to that one is much larger.

WOuld the 12 3 work for a 5 Hp?

Yes, the 50 amp circuit would work for the 7.5 hp.

You'd probably need a 40 amp for the 5 hp, but that 12 ga cable is too small.


Posted from Garagejournal.com App for Android
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Yes, the 50 amp circuit would work for the 7.5 hp.

You'd probably need a 40 amp for the 5 hp, but that 12 ga cable is too small.


Posted from Garagejournal.com App for Android

If the wire was sized based on a welder using the circuit, the wire might be too small as circuits feeding welders are allowed to be reduced in size!!
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Distance does come into play but usually at distances greater than 100'. So for typical circuits within a house distance is not a wire size adjustment issue.

Perhaps I missed it but wire size depends on the distance run as well as the amps.
 
To avoid these ads, REGISTER NOW!

ez-duzit

Well-known member
Joined
Jun 24, 2013
Messages
5,094
Location
Marina del Rey
Distance does come into play but usually at distances greater than 100'. So for typical circuits within a house distance is not a wire size adjustment issue.

Sorry, but I beg to differ.

62425d1235669252-wire-gauge-ampacity-table-wiringdiagram.jpg
 

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
Nice try but thats for 12v DC wiring which is a whole different animal than AC wiring!

If that table 'was' for AC.....none of us would be able to have anything larger than 100A at our house..

There are actually two tables for AC wire current....one is referenced to AC Transmission....the other is chassis wiring (control panels).

And then you have the NEC table for AC power distribution....which is sort of in between the above 2.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I'm not following what you want to beg to differ about? I didn't say wire size didn't need to be adjusted for distance. I agree that it does. I'm just saying over sizing wire for voltage drop typically doesn't come into play until you reach lengths of 100' or more for the average household circuit and even then it depends on the anticipated loads.

Sorry, but I beg to differ.
 

RickP

Well-known member
Joined
Jan 15, 2013
Messages
1,548
Location
Annapolis, MD
If the wire was sized based on a welder using the circuit, the wire might be too small as circuits feeding welders are allowed to be reduced in size!!

Good call -- for an extreme case (like a large motor or a long wire run).
But for the OP (who hasn't bought a compressor yet), I think chances are pretty good that the 50A circuit will be perfect for a 7.5 hp compressor. He'll definitely need to check his wire size to be sure it wasn't sized for a welder, but unless it's an extreme case, that 50A circuit should be adequate for a 7.5 hp motor (or less).

I say this because Joe's friend probably ran 6 AWG cable for that 50 amp circuit, if not, then it's gotta be 8 AWG (because it's "much larger" than the #12 Romex). A big box compressor will probably use a motor with FLA of about 32A -- post #9 here: http://www.garagejournal.com/forum/showthread.php?t=131410 -- which means 125 percent of the FLA is going to be right at 40A, so that would need 8 AWG cable. If he hardwires the comp to a disconnect, then I believe the NEC allows a 50A breaker on that circuit.

Please let me know if I have any of that wrong, because I'm hoping I can hardwire my 5 hp comp with 10 AWG cable and a 40A breaker.

Thanks,
Rick
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
If using romex, #10 NM-b is 30A max and #8 NM-b is 40A max. Being hardwired has noting to do with the breaker size. If you use THHN in conduit then #10 THHN is 35A and #8 THHN is 50A. The difference is romex is to be sized at 60 deg.C and THHN is sized at 75 deg.C.

Good call -- for an extreme case (like a large motor or a long wire run).
But for the OP (who hasn't bought a compressor yet), I think chances are pretty good that the 50A circuit will be perfect for a 7.5 hp compressor. He'll definitely need to check his wire size to be sure it wasn't sized for a welder, but unless it's an extreme case, that 50A circuit should be adequate for a 7.5 hp motor (or less).

I say this because Joe's friend probably ran 6 AWG cable for that 50 amp circuit, if not, then it's gotta be 8 AWG (because it's "much larger" than the #12 Romex). A big box compressor will probably use a motor with FLA of about 32A -- post #9 here: http://www.garagejournal.com/forum/showthread.php?t=131410 -- which means 125 percent of the FLA is going to be right at 40A, so that would need 8 AWG cable. If he hardwires the comp to a disconnect, then I believe the NEC allows a 50A breaker on that circuit.

Please let me know if I have any of that wrong, because I'm hoping I can hardwire my 5 hp comp with 10 AWG cable and a 40A breaker.

Thanks,
Rick
 

RickP

Well-known member
Joined
Jan 15, 2013
Messages
1,548
Location
Annapolis, MD
pattenp said:
If using romex, #10 NM-b is 30A max and #8 NM-b is 40A max. Being hardwired has noting to do with the breaker size. If you use THHN in conduit then #10 THHN is 35A and #8 THHN is 50A. The difference is romex is to be sized at 60 deg.C and THHN is sized at 75 deg.C.

Okay, now I'm confused -- I thought the NEC allows the breaker to be oversized (compared to a smaller wire size) for a hardwired motor, to allow for startup current draw???

So for a normal circuit, I would use a 30A breaker to protect 10 AWG cable. But for a hardwired motor, I can use a 40A breaker instead. Does that sound right?

Thanks,
Rick



Posted from Garagejournal.com App for Android
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
Okay, now I'm confused -- I thought the NEC allows the breaker to be oversized (compared to a smaller wire size) for a hardwired motor, to allow for startup current draw???

So for a normal circuit, I would use a 30A breaker to protect 10 AWG cable. But for a hardwired motor, I can use a 40A breaker instead. Does that sound right?

Thanks,
Rick



Posted from Garagejournal.com App for Android

Because for NM cable the NEC limits it to the 60 degree C ampacity which means,14 AWG is 15A, 12 AWG is 20A, & 10 AWG is 30A, but w/ THHN conductors, for a motor circuit meeting the requirements of art 430 of the NEC, 14 AWG is 20A,12 AWG is 25A, & 10 AWG is 35A. Please note : These in no way apply to normal branch circuits!!!!
 
OP
J

JOE.G

Well-known member
Joined
Feb 4, 2013
Messages
765
Location
Eastern ( Catskills ) NY
So you guys are saying I should take the 50 Amp breaker out and put either a 30 or 40 amp breaker?

Also when you get a new compressor does it come with a wire to hook to the wall?
Can I put a plug on the end or does it need to be hard wired?

How many amps can 12 3 Romex take?
 

ez-duzit

Well-known member
Joined
Jun 24, 2013
Messages
5,094
Location
Marina del Rey
Forget 12-3.

The new compressor will probably not have a plug and cable but will surely have a manual explaining the electrical connection.

If your 50 amp circuit was wired correctly, just leave the breaker that's there; it will protect that circuit.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
So you guys are saying I should take the 50 Amp breaker out and put either a 30 or 40 amp breaker?

Also when you get a new compressor does it come with a wire to hook to the wall?
Can I put a plug on the end or does it need to be hard wired?

How many amps can 12 3 Romex take?

#12 NM-B(aka brand name Romex) is limited to 20a(60c deg ampacity column) regardless of the number of conductors in the cable. Sorry! 12-3 NM-B is just not gonna cut it for your compressor!
 

Mr onetwo

Well-known member
Joined
Apr 6, 2011
Messages
2,006
Location
Coastal Maine
The manual for my 1977 IR T30 253 compressor states that for a 5HP motor you are to use #8 THHN or equal up to 100ft.You are to size the breaker at 3 times motor FLA up to a maximum of 70AMP.The FLA of my Baldor motor is 20.6 so I put this circuit on a 60AMP breaker.It has been stated correctly that the sizing for NMB is different.I have a brand new Eaton 30AMP single phase mag starter and the directions that came with it are exactly the same 35 years later.I am not smart enough to contradict these instructions:dunno:
 

Spudland_Dave

Well-known member
Joined
Mar 12, 2010
Messages
3,025
Location
Maine
Good timing...My compressor is not a 7.5hp, For the time being I only have a 3hp...BUT I am about to start wiring it in the next few days. I WAS Gonna use 40A on #8 Romex...BUT now I'm second guessing myself in terms of future proofing.

If NEC Says a 7.5HP is 40A, is the 125% uprating for the purposes of Continuous duty? ie 3hours or more @ 100% utilization?
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
If you think you'll have a comp with a 7.5hp rated motor you should use the 125% and put in a 50A circuit.

Good timing...My compressor is not a 7.5hp, For the time being I only have a 3hp...BUT I am about to start wiring it in the next few days. I WAS Gonna use 40A on #8 Romex...BUT now I'm second guessing myself in terms of future proofing.

If NEC Says a 7.5HP is 40A, is the 125% uprating for the purposes of Continuous duty? ie 3hours or more @ 100% utilization?
 

greenbluff garage

New member
Joined
Jul 7, 2012
Messages
4
Location
colbert wa
I just bought the sears 5hp (5.4) 80 gal compressor you were looking at. I used #10 wire and a 30 amp fuse. the compressor is 22 amp. I was told by an electrician that the compressors amps should be 80% of the fuses capacity, so 30 amp is more then enough. If you run your wire longer then 75 feet you will have to up size the wire. :thumbup:
 