No, unless the short is inside the motor itself. The circuit breaker covers anything that happens upstream of the internal overload protection.

Not for a motor circuit.

The overloads in the motor starter or integral motor overloads protect the circuit wiring.

The circuit breaker only protects against short circuits and ground faults... In other words, it doesnt protect the wire from overload...
 
To avoid these ads, REGISTER NOW!

TRWham

Well-known member
Joined
Aug 11, 2017
Messages
1,958
Location
East Cobb County, Georgia
Not for a motor circuit.

The overloads in the motor starter or integral motor overloads protect the circuit wiring.

The circuit breaker only protects against short circuits and ground faults... In other words, it doesnt protect the wire from overload...

I was answering the question of protection against short circuit, not overload. The internal overloads could not detect a short in the conductor before the motor. No current would reach the motor.
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
No, unless the short is inside the motor itself. The circuit breaker covers anything that happens upstream of the internal overload protection.

This is what I meant, does the internal thermal protect against short in the motor,,, it's called thermal not short? I spose it would, this would allow smaller motors on larger circuits provided the primary wiring was big enough for short.
 
To avoid these ads, REGISTER NOW!
Top Bottom