To avoid these ads, REGISTER NOW!

240 V electrical

To avoid these ads, REGISTER NOW!

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,078
SMH You should read up on the differences between overload protection and over current/short circuit protection in motor circuits.
I've got a motor with a Rockwell Jam protection (high overload) relay on it, in addition to the starter.
 

djbmw

Well-known member
Joined
Jun 20, 2013
Messages
1,238
Location
Ottawa, Ontario, Canada
seriously? :shocking: :dunno: :ROFLMAO::lol_hitti
I said that because mm08822 referenced one of my previous comments. I had said that a 15 amp 2 pole breaker could also double as an overload and overcurrent device on this motor, as long as it DOES NOT trip with inrush current.

So... it was pointless to then talk about it tripping,.. but thats where the conversation went/continued... so I joked that if it continually tripped with inrush then the lift wouldnt work anyway.

*shrugs*
 
OP
M

MikeC55

Well-known member
Joined
Nov 1, 2020
Messages
452
Location
CT
A couple more questions on upgrading the (100 amp, 6 circuit) sub-panel in detached garage. Since the new panel has room for 20 circuits and I plan to use more than 6, I think I'll need a main breaker that allows shutting power to the whole sub-panel without having to go into the house to main panel feed. Makes sense if you need to shut the garage down in a hurry. Looking at the panel I bought (which is intended to be a sub-panel), I don't think I can install a main disconnect breaker in the panel; it would need to be another small box for just the main shut-off breaker which then feeds this sub-panel. It also seems that in CT, for a detached garage using a sub-panel, I would need to install a grounding rod (even though neutral and ground are separated, as they should be for a sub-panel). The electrician who installed the original sub-panel, did not install a ground rod. I'm curious if you would expect any ground loop issues if your ground bar in the sub-panel is connected to both, the main panel ground wire and the new ground rod (next to garage)?
 

Attachments

  • IMG_1151.jpeg
    IMG_1151.jpeg
    651.5 KB · Views: 11

Cruzan80

Well-known member
Joined
Jul 22, 2015
Messages
4,485
Location
Denver, CO
It also seems that in CT, for a detached garage using a sub-panel, I would need to install a grounding rod (even though neutral and ground are separated, as they should be for a sub-panel). The electrician who installed the original sub-panel, did not install a ground rod. I'm curious if you would expect any ground loop issues if your ground bar in the sub-panel is connected to both, the main panel ground wire and the new ground rod (next to garage)?
Yes, any detached structure with a subpanel should have both grounding rods as well as connecting to the "supply" panel's ground via wire. I will let other, more knowledgeable people chime in with the why (I understand it, but can't explain it via text as well as others I have seen on here do it).

IIRC, the ground rods are subject to the same requirements as a main (if only one, you need to measure and ensure something, so most people just drive two as there is no measuring involved in that case).
 

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,911
Location
Southern Oregon
A couple more questions on upgrading the (100 amp, 6 circuit) sub-panel in detached garage. Since the new panel has room for 20 circuits and I plan to use more than 6, I think I'll need a main breaker that allows shutting power to the whole sub-panel without having to go into the house to main panel feed. Makes sense if you need to shut the garage down in a hurry. Looking at the panel I bought (which is intended to be a sub-panel), I don't think I can install a main disconnect breaker in the panel; it would need to be another small box for just the main shut-off breaker which then feeds this sub-panel.

That's a SqD Homeline panel.
You can get a main breaker for it.
Replace the main lugs with a QOM100VH (assuming you've got a 100A or less feed).

 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,250
Location
Modesto, CA
It also seems that in CT, for a detached garage using a sub-panel, I would need to install a grounding rod (even though neutral and ground are separated, as they should be for a sub-panel). The electrician who installed the original sub-panel, did not install a ground rod.

2 ground rods are actually required. the electrician that installed the subpanel didnt know what they were doing

I'm curious if you would expect any ground loop issues if your ground bar in the sub-panel is connected to both, the main panel ground wire and the new ground rod (next to garage)?

no such thing as a ground loop between grounding electrodes. why? because under normal circumstances, there is no current flowing on ground rods. even there were, there would be no such thing as a ground loop because current returns to its source. it would circle around between grounding electrodes. ground loops is something that happens in audio systems...
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,607
Location
SE MI
ground loops is something that happens in audio systems...
It happens in cars also ! Run a wire from the negative post of the battery to the back of the vehicle. Check for voltage between the wire and the frame.

That is not a "real world" example, but it does happen. One common mistake is to connect both ends of a braided shield to "ground".
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,370
Location
Coastal NJ
Not really. It you have a neutral and L1, L2 you have 120/240.
If you ask an electrician to run a 240V circuit in your house and he leaves out the unnecessary neutral.....
You got what you asked for. If you ask for a dryer receptacle, you get 120/240.
 
To avoid these ads, REGISTER NOW!

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,607
Location
SE MI
If you ask an electrician to run a 240V circuit in your house and he leaves out the unnecessary neutral.....
You got what you asked for. If you ask for a dryer receptacle, you get 120/240.
Then you had better specify the outlet type (NEMA) or at least the item that will use it !
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,607
Location
SE MI
Long ago ...

I purchased a commercial high volume laser printer for my company. I asked that the electricians install a 240v outlet (probably a 6-20R or a 14-20R). I don't remember what they actually installed, but it was not what I requested ! Then I was told, (most) commercial building don't have 240VAC, only 208VAC !

Luckily the equipment had a multi-tap input transformer !
 

mikedodge

Well-known member
Joined
Jun 27, 2017
Messages
2,965
Long ago ...

I purchased a commercial high volume laser printer for my company. I asked that the electricians install a 240v outlet (probably a 6-20R or a 14-20R). I don't remember what they actually installed, but it was not what I requested ! Then I was told, (most) commercial building don't have 240VAC, only 208VAC !

Luckily the equipment had a multi-tap input transformer !

Usually most things that run that voltage specifically list input voltage is 208-240V for that very reason. And to your other reply before that they also usually say the NEMA outlet type. Here's a random Xerox spec for example:

  • North America: 208–240 V, 50/60 Hz, 16 amps; requires 20A circuit, NEMA 6-20-R socket
  • Europe: 220 –240 V, 50 Hz, 20 amps/requires 20A circuit, PCE Shark 023-6 mating socket
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,136
Location
Central Iowa
Then you had better specify the outlet type (NEMA) or at least the item that will use it !
The customer had better specify the NEMA configuration. If you tell me you need a 20 amp twotwenny, that's exactly what your going to get. Tell me it's 120/240, four wire (counting the ground), or it needs a neutral and that changes things. There is no 240 load that needs a neutral.
 

Cruzan80

Well-known member
Joined
Jul 22, 2015
Messages
4,485
Location
Denver, CO
2 ground rods are actually required. the electrician that installed the subpanel didnt know what they were doing
Wylie, is it automatic that a detached structure needs two, or is it able to use one as long as it is measurable to a specific amount (IIRC, resistance to ground?), just like a main?

I know most people automatically jump to installing 2x, as there is no measurement needed, but wasnt sure if one was allowed at all on a detached subpanel.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,250
Location
Modesto, CA
Then you had better specify the outlet type (NEMA) or at least the item that will use it !

what happens when its hard wired?

you dont need to specify the receptacle. a 240v circuit that has auxiliary items that run on 120v would be specified as a 120v/240v circuit NOT a 240v circuit. not sure why this is so hard to grasp.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,250
Location
Modesto, CA
Wylie, is it automatic that a detached structure needs two, or is it able to use one as long as it is measurable to a specific amount (IIRC, resistance to ground?), just like a main?

I know most people automatically jump to installing 2x, as there is no measurement needed, but wasnt sure if one was allowed at all on a detached subpanel.

you can use 1 grounding electrode but you have to have the equipment to prove 25ohms or less. i doubt you have the equipment which costs a lot of money
 

Cruzan80

Well-known member
Joined
Jul 22, 2015
Messages
4,485
Location
Denver, CO
you can use 1 grounding electrode but you have to have the equipment to prove 25ohms or less. i doubt you have the equipment which costs a lot of money
Agreed. I was just trying to make sure that I had the rules straight in my head, and the requirements didn't change from the main to a detached subpanel (not sure why it would, but also not my main job). I put in two when I did my garage. Thanks.
 
OP
M

MikeC55

Well-known member
Joined
Nov 1, 2020
Messages
452
Location
CT
For my 100 amp sub-panel discussed here, what size wire do I need to attach the ground rods to ground bar? I’ve been digging, but can’t find it…
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,136
Location
Central Iowa
#6 solid cu doesnt need protection. #8 does
For my 100 amp sub-panel discussed here, what size wire do I need to attach the ground rods to ground bar? I’ve been digging, but can’t find it…
Depending on the jurisdiction, we might have to use #6 as a minimum but if it isn't protected it's #4. I automatically use 4 everywhere.
 

JohnX14

Well-known member
Joined
Jun 2, 2014
Messages
683
Location
Boston 'burbs
We use #6 stranded to ground rods.

I'll agreed that you will never get under 25 Ohms to ground with ground rods. But I'll "argue" that the 2nd ground rod adds no value., despite being required by code. Although I don't think it's much of an argument, almost everyone in the industry agrees.
 
To avoid these ads, REGISTER NOW!
Top Bottom