Background: want to have future capability to install 2pc - 24kBTU minisplits when money becomes available. Only have 2 slots (for 1pc double pole breaker) in my shop's panel available.
I picked up a 4-slot (for 2 double pole) main lug panel at Menards over the weekend to be a subpanel within the same conjoined structure.
I don't need the neutral for my power requirements, however, is there any requirement to run it back? I'm wanting to just run red, black, and ground.
Im thinking I want #6 THHN feeding from 50A breaker in shop panel to the new main lugs and eventually a couple of 25As in the 4-slot. Not 100% sure what the A/C requirements will be but hopefully I'm being conservative.
Thanks!
I picked up a 4-slot (for 2 double pole) main lug panel at Menards over the weekend to be a subpanel within the same conjoined structure.
I don't need the neutral for my power requirements, however, is there any requirement to run it back? I'm wanting to just run red, black, and ground.
Im thinking I want #6 THHN feeding from 50A breaker in shop panel to the new main lugs and eventually a couple of 25As in the 4-slot. Not 100% sure what the A/C requirements will be but hopefully I'm being conservative.