240vac Only Subpanel

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,725
Location
SE Michigan
Background: want to have future capability to install 2pc - 24kBTU minisplits when money becomes available. Only have 2 slots (for 1pc double pole breaker) in my shop's panel available.

I picked up a 4-slot (for 2 double pole) main lug panel at Menards over the weekend to be a subpanel within the same conjoined structure.

I don't need the neutral for my power requirements, however, is there any requirement to run it back? I'm wanting to just run red, black, and ground.

Im thinking I want #6 THHN feeding from 50A breaker in shop panel to the new main lugs and eventually a couple of 25As in the 4-slot. Not 100% sure what the A/C requirements will be but hopefully I'm being conservative.

Thanks!
 
Last edited:
To avoid these ads, REGISTER NOW!

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,309
Location
Dutzow Missouri
Do you really want to be that guy?

Years from now we will be reading the post
“Who installs a sub panel without a neutral????”

I say if you can’t do it right or do not do it.

How much will you save? $10 or 20

Walta
 
OP
M

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,725
Location
SE Michigan
Do you really want to be that guy?

Years from now we will be reading the post
“Who installs a sub panel without a neutral????”

I say if you can’t do it right or do not do it.

How much will you save? $10 or 20

Its a good point but I have a 120vac exterior outlet close by already, fed by another circuit.

Yes, the 4 slot does limit expansion but I feel like I'm close to maxing out the amperage anyway based on the "potential" for what the double A/Cs can draw.

What size would I run on the neutral, another #6 awg? That seems wasteful plus something additional I'd have to buy....I'm going to guess its 30 feet of wire, I'm going to guess $1.50/ft at "buy by the foot" section of HD.
 

Bretny

Well-known member
Joined
Jul 31, 2017
Messages
3,918
Location
Dutchess county NY
So your alreaty having to add a sub pannel and your wanting to limit your self again? Power it like a regular sub pannel alreaty.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
While you would leave a bit of option by adding a wire doent mean you need to and there is nothing like a simple box dedicated to equipment disconnect. Makes it plain as day, know someone didn't energize thru another wire etc.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
One of the reasons you may not want a N is you don't want people tapping this. On occasions we see recommendations for inch pipe and electric boxes but I got 6000 sq ft and nothing over 3/4 for branch circuits. One place I ran a separate 3/4 a section for a welder, its own pipe, doesn't all got to be in one. I have a couple shared with 10 for small wire feeders and although I do have a 300 tig I have never had to plug it in my wire welder circuit. All its own for that too.
In the cases of shared pipe it keeps 2 current conductors out, reduces the fill and any need for derating etc. In the case of welders could change breakers for tailored circuits if it needed, big if, but nothing is as good as single circuit in a pipe.
 
Last edited:

Mr_fixit

Well-known member
Joined
May 24, 2008
Messages
1,221
Location
Rustylvania
Background: want to have future capability to install 2pc - 24kBTU minisplits when money becomes available. Only have 2 slots (for 1pc double pole breaker) in my shop's panel available.

I picked up a 4-slot (for 2 double pole) main lug panel at Menards over the weekend to be a subpanel within the same conjoined structure.

I don't need the neutral for my power requirements, however, is there any requirement to run it back? I'm wanting to just run red, black, and ground.

Im thinking I want #6 THHN feeding from 50A breaker in shop panel to the new main lugs and eventually a couple of 25As in the 4-slot. Not 100% sure what the A/C requirements will be but hopefully I'm being conservative.

Thanks!

I'd take back what you bought. And save your money, for now. When you have the money for the a/c, I'd suggest thinking about what you might really need to add, electrically , for the home in the next 10 years or more. I don't think using the last 2 slots to solve the A/C problem would be a good long term solution. Maybe a different location for a sub, or a larger sub, or a larger service. Adding A sub off the sub? What happens when you need room to add a small heater, kitchen receptacle or basement fridge, etc?
 
OP
M

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,725
Location
SE Michigan
I'd take back what you bought. And save your money, for now. When you have the money for the a/c, I'd suggest thinking about what you might really need to add, electrically , for the home in the next 10 years or more. I don't think using the last 2 slots to solve the A/C problem would be a good long term solution. Maybe a different location for a sub, or a larger sub, or a larger service. Adding A sub off the sub? What happens when you need room to add a small heater, kitchen receptacle or basement fridge, etc?

Your points are good, I'm preparing to hang drywall shortly. I plan to wire NMb into the stud cavity, then thru the wall to AC disconnects on the outside wall, and that will all be done before drywall. Waiting for next year, would put me into a project that would require moving heavy equipment stationed near the wall and then tearing back into the recently finished drywall. So this is an effort into future proofing so I won't have to do either of those.

I do have extra panel spaces where needed but this part of the shop is pretty mature at this point. If I had 4 spaces available I'd probably already be working instead of posting :)
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
There are cases where local disconnect is required. This cost an extra breaker but saves 2 at the main and gives disconnecting means with overcurrent right next to the units.

I could go either way on this but I liked the description,,, mature and this circuit could be purely dedicated to equipment. Its not a bad thing. I would probably put 6 spaces cause,,, I can and stock a panel.
 

Marctrees

Well-known member
Joined
Mar 5, 2015
Messages
6,265
Location
TX/LA border - Toledo Bend
Matt - May want to call your local Electric Supply houses... tell hem cash sale, no account...I just did that few days ago for a 4 piece total 248' of ? THWN ? wire for a 100 amp sub,

Total was approx 25 % less than Lowes.

Marc
 

Milton Shaw

Well-known member
Joined
Feb 11, 2011
Messages
4,835
I just ran a 60 amp 6 space sub-panel for my wife's new kiln. It draws 38 amps at 240 volt so I put in a circuit with #6 /3 with ground. She has already in one month decided she wanted a 120 volt kiln and bought one that draws 15 amps for smaller stuff. I am glad I ran 6/3 w/g so that all I had to do was add an outlet and breaker to the 6 place box I put in. She has gotten in to slumping glass as an addition to her stained glass work . Very interesting and creative woman I married. She has the patience to do art glass when something inspires her.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,467
Location
Richmond, VA
I just ran a 60 amp 6 space sub-panel for my wife's new kiln. It draws 38 amps at 240 volt so I put in a circuit with #6 /3 with ground. She has already in one month decided she wanted a 120 volt kiln and bought one that draws 15 amps for smaller stuff. I am glad I ran 6/3 w/g so that all I had to do was add an outlet and breaker to the 6 place box I put in. She has gotten in to slumping glass as an addition to her stained glass work . Very interesting and creative woman I married. She has the patience to do art glass when something inspires her.

This isn't for a workshop. Apples and oranges
 

nh_yota

Well-known member
Joined
Mar 10, 2015
Messages
4,076
Location
Seacoast New Hampshire
If you're down to only one 2P breaker space you should add a regular 120/240 subpanel anyway in case you want to add more circuits in addition to the new ones for the AC units.
 