huh?To bad they don't offer either 208 or 240/ 3 ph
huh?To bad they don't offer either 208 or 240/ 3 ph
Sticking with NEMA motors, 208v is fine as it is the -5% value of 230v. The real question is, does any mfr build in any reserve to a motor rated 208-230 to handle 208v - 5%, or is the 208v value simply the lower limit of 230v and the rest is just a marketing answer to the q "can this 230v motor run on 208v?"
Oh duh!! yes 10%. I'll fix that.You summed up what I was trying to say earlier in a much easier question.
By the way, do you mean 208(207 actually) is 10% and not 5% of 230?
Sticking with NEMA motors, 208v is fine as it is the -10% value of 230v. The real question is, does any mfr build in any reserve to a motor rated 208-230 to handle 208v - 5/10%, or is the 208v value simply the lower limit of 230v and the rest is just a marketing answer to the q "can this 230v motor run on 208v?"
I'm talking about is there any reserve built into a 208-230v rated motor @ the less than 208v level. I'm not confusing that with SF.Some 208-230/460 motors have reserve built into them, others do not. It depends on the service factor. If the SF is 1.0, there's no reserve, it it's higher (like 1.15) then there is.
Basically, service factor goes like this......if a 10HP motor has an SF of 1.15, it is an 11.5HP motor marketed as 10HP. Provided its design parameters are not exceeded, it will produce 11.5HP continuously.
If the SF is 1.0, it is a 10HP motor marketed as 10HP and if it is made to produce more than 10HP, it'll burn up.
Some manufacturers will have a 230/460 rating and a separate 208 rating. The 208 rating usually has higher current, sometimes lower RPM and sometimes lower SF.
We had this happen once. Had a automatic gate opener installed by a contractor. They provided all the wiring from the panel to the opener and unknowingly landed the breaker on the "open spot" of the 3rd leg. The control board did no like that.most likely to prevent burning up 120v equipment which can happen when someone connects it to the stinger/hi leg.
having a separate panel for 120v loads prevents the hi-stinger leg from ever being part of the equation...
200V is the rated voltage for 208V, just like 230/460V is is the rated voltages for 240/480V. While the 200V rating has been around for a while, I have a couple of Rockwell machines with 200V motors from the early 1970's, NEMA changed the rating from 208V to 200V a few years back. So the current rating for a tri-volt motor is 200-230/460V.I'm talking about is there any reserve built into a 208-230v rated motor @ the less than 208v level. I'm not confusing that with SF.
SF is as you describe above but determined by mfr only at rated voltage and frequency and for intermittent overloads. To me that means at 230 or 460v. If there was a SF rating @208v, then it wouldn't apply @ 200v for example.
Guess I'm the odd man out.
Your post has a error, wye systems do not have a wild leg, delta does though.I have experience with both Wye and Delta systems.
With Wye systems there is a “Wild Leg” that can burn up a piece of 120 Volt equipment if you mistakenly hook up to it. I was not aware of that and the panel was not marked. Additionally the Wild Leg was not identified with Orange Tape. Fortunately I was not required to replace the radio that burned up, but I made sure to identify the wild leg and added a warning label to the panel about the wild leg.
120 Volts bites but 277 kicks, I am very happy that I no longer have to work 277 circuits Hot.
Thanks for setting me straight. It’s been over 20 years since I last worked on a 3 Phase system.Your post has an error, wye systems do not have a wild leg, delta does though.
When I was in the HVAC compressor manufacturing business, we tested all motors to +- 5% of the nameplate. If it was shown as a spread voltage motor then it was tested to 5% below 208 V (197 V) and 5% above 230 V (242 V). Obviously, it would draw more current at the lower voltage at the same load, but that is just physics at work. Most motors were rated for 50 and 60 Hz as well, but at different voltage. Before that, I worked for an equipment manufacturer, and the vast majority of the systems we built were installed in 208/3 buildings.I wouldn't go 208. A lot of equipment that is rated for 208 or 230 is given that nameplate, but runs like trash at 208. It very well might overheat or the Ip will cut out the power. If the voltage sags on the island it might not run at all, see rural NY. If you do go 208 make sure the equipment was designed for 208, not was designed for 230 and also runs on 208.
I test 3 phase equipment for a living.
you got it backwards. Delta has the stinger leg- 120/208/240 are the voltages on 4-wire deltaI have experience with both Wye and Delta systems.
With Wye systems there is a “Wild Leg” that can burn up a piece of 120 Volt equipment if you mistakenly hook up to it. I was not aware of that and the panel was not marked. Additionally the Wild Leg was not identified with Orange Tape. Fortunately I was not required to replace the radio that burned up, but I made sure to identify the wild leg and added a warning label to the panel about the wild leg.
120 Volts bites but 277 kicks, I am very happy that I no longer have to work 277 circuits Hot.
why are they changing the trany bank in the first place? old?I got a call today from a customer that makes well drilling and directional boring equipment in a factory that hasn't changed a thing since the 50's. The POCO wants to change out the 240D transformer and replace it with 208. In this case, I told him to tell them no and to leave it alone until they find the right transformer, which apparently it tougher than it should be. They have a plasma table and a CNC machine that I had to put buck-n-boost transformers on, but I don't remember if they are bucking or boosting due to low voltage. They also have a bunch of equipment I haven't touched that dates back to WWI that might not like 208.
That would be my guess. The GM is who called me, but couldn't answer my questions of why they want to change it to begin with or the reasoning behind the 208.why are they changing the ****** bank in the first place? old?
Same here.The PUCO around here is a lot like an overgrown schoolyard bully.....
Does the POCO typically change a 3 phase transformer and not let you know? I am almost certain years ago when we built the shop we had 240v. The other day I was checking the power to a lathe I plan on moving and converting over to a VFD to operate it on single phase power at my home shop. When I checked the power I had 2-120v legs and 1-208v leg. Its not how I remember it.

That is 240 three phase. Line to line between any two of the three will be 240.Does the POCO typically change a 3 phase transformer and not let you know? I am almost certain years ago when we built the shop we had 240v. The other day I was checking the power to a lathe I plan on moving and converting over to a VFD to operate it on single phase power at my home shop. When I checked the power I had 2-120v legs and 1-208v leg. Its not how I remember it.
Thats 240v deltaDoes the POCO typically change a 3 phase transformer and not let you know? I am almost certain years ago when we built the shop we had 240v. The other day I was checking the power to a lathe I plan on moving and converting over to a VFD to operate it on single phase power at my home shop. When I checked the power I had 2-120v legs and 1-208v leg. Its not how I remember it.
Or is it that there are not always both options available, and any 3ph option is better than no 3ph?
You would have to use single pole 277V breakers on the high leg, which opens up more issues.You cant use the hi-leg for line to neutral loads
The voltage is not stable and running a load on it can cause weird imbalances.
You would also have to use straight rated breakers because of the higher voltage to neutral/ground.
why would it have to be 277v rated breakers? 240 straight rated breakers should workYou would have to use single pole 277V breakers on the high leg, which opens up more issues.
Because they don't make 240V single pole breakers.why would it have to be 277v rated breakers? 240 straight rated breakers should work
Aaawww i admittedly have never searched for a straight rated single pole breaker… because well Ive never needed to…Because they don't make 240V single pole breakers.
347/600Y service is a Canadian voltage.Your 3-phase options are 120/208Y or 347/600Y.
Last thing you would want to do is run a 230V compressor on 208V. When ordering a new compressor, I-R supplies a single voltage motor when 208V is specified, IMHO, if 3Ø power is available, it's foolish not to use it.Lot of machine tools I've run into are 240v 3 phase. Is 208v enough?
For just 2 air compressor motors, single phase would be the most logical to me, unless you only have 125 amp service like here.
347/600Y service is a Canadian voltage.
If he's doing work in the US it's 277/480Y
Last thing you would want to do is run a 230V compressor on 208V.
In the Northeastern US, some POCOs get their power generated from Canada.Common yes, exclusively Canadian, no.